PV Grid Tied Inverter System Not To Export, Can this be Done?ch nhveng ng
Hi all,
I have a customer with 300 KW PV inverter system and they are planning to interconnect such to the grid. Their equiopment is not IEEE 1547 or UL 1741 tested for grid intertie.
I am thinking that if their inverter capacity or maximum output is less than the peak load or the inverter output can reduce current output during light loading to prevent export to utility, then it would eliminate complicated requirements for interconnection. However, is there an inverter that does that?
Alternatively, I was also thinking about splitting the PV-fed AC panelboard from normal utility panelboard and apply open transition tie contactors in the event PV is insufficent to power local loads. But I am looking for a seamless way of connecting inverter and utility without exporting so that the PV system is only for minimizing utility import only.
RE: PV Grid Tied Inverter System Not To Export, Can this be Done?ch nhveng ng
Here is one unit. Beware this will not work properly on unbalanced lines. Not suitable for a 240 Volt inverter on a 120:240 Volt system.
There was a recent thread that explored this option.
thread248-430843: Solar grid tie battery
Look towards the end of the thread.
Bill
"Why not the best?"
Jimmy Carter
I forgotto mention in my OP that the 300 kW “inverter” is actually 3 x 100 kW smaller inverters.
If I follow the case at the end of the thread, assuming the inverter group control system is able to load share, each inverter will have utility inputs and the outputs will be connected to a common bus. As I understand the thread, I am thinking as follows:
1. Each 100 kW PV system group connected to each inverter DC bus inverter
2. Each inverter will somehow be programmed to operate directly from PV
3. In the event of low PV output or evening, power will be taken from utility
4. Option to provide battery bank on each inverter with PV charging the battery bank and supplying power to DC bus for loads....in this case need larger PV capacity
Is this understanding of mine on the thread sound right?
On the other hand, what about having a smart meter to compare load vs PV generation and when PV generation > loads, will execute command to shed PV generation via PV solar cell disconnection or inverter output limitation?
Or use load bank during light loading?
Many stuff in mind, none proven to work perhaps today.
Have the inverters been purchased?
What voltage are you connecting at?
Are we discussing single phase inverters or three phase inverters.
If you are retrofitting an existing installation it becomes very challenging.
If you already have the inverters, what is the make and model?
Bill
"Why not the best?"
Jimmy Carter
The service voltage for the loads is 600 V, the utility service is coming from 34.5-0.6 kV Delta-Wye grounded, step down transformer. The 600 V system will be 3 phase 3 wire, 60 Hz from solidly grounded system.
I am a bit confused of your statement:
“If you can connect the inverters for 277 Volts or 347 Volts and use one on each phase of a 277:480 or 347:600 Volt service it may work well.”
A sketch SLD may help me understand what you are getting at
Many thanks, star for you.
A neutral will be available if you chose to connect it.
Your line to neutral voltage on a 600 Volt system will be 347 volts. Three inverters could be connected from the line to neutral.
Bill
"Why not the best?"
Jimmy Carter
Most of the utilities here have set an arbitrary figure of 30kW, above this figure, standards compliance and / or additional protection is required. Quite a number of manufacturers make protection relays for this application, though whether they're suitable for use in terms of IEEE 1547 or UL 1741 I don't know.
At that sort of scale of inverter, it should be possible to arrange for some sort of power metering that is capable of interacting with the inverters in order to regulate the output so as to not export to the network. Ideally the inverter manufacturer already has a suitable product. At about 100kW per inverter size, in my experience they'd be 3 phase rather than single phase, along with all the considerations of a grounding system for a 3 phase connection (the last inverter I saw that size was ungrounded, and had IEEE 1547 compliance. It relied on DC bus ground fault detection, and needed an isolation transformer to connect it to the network).
I'd also imagine that the relevant utility and what they permit will have a great influence over what you can do. I can also advise that attempting to use equipment not compliant with standards often gets far more expensive, particularly when additional equipment is mandated by the utility as a result.
EDMS Australia
Also, what is the minimum load in you facility. I've seen systems where the inverter is connected through a shunt trip breaker and the installer places a reverse power flow relay at or near the service entrance. If the power flow goes negative, the relay trips the inverter breaker.
JFPE
EDMS Australia
Link
There is a 600 Volt model available.
Contact the manufacturer for information on running three units in no-export mode on the same system.
Bill
"Why not the best?"
Jimmy Carter
As they are following Grid voltage for their output reference, they must not actively regulate voltage at the PCC.
Having metering that actively senses the local loads they serve and communicates with the inverters to somehow “shed” generation will be ideal and a reverse power relay that will trip the main breaker at PCC will work as well.
I do not know up to how much reactive or active power can be backfed without affecting the Distribution Utility, I do not have such specified in any of their standards.
You will need each of the three inverter AC outputs to be separately and permanently wired to their own part of the breaker panel with their output never to be connected.
eg: With voltage drops, one line has 120 Volts and the other line has only 114 Volts, The meter would assume that each lines had 114+120/2= 117 Volts.
The heavy load would be metered at 117/114 Volts or 102%.
The light load would be metered at 117/120 Volts or 97.5%
This was not a lot of error and was in the favour of the utility.
There was a scheme to meter unbalanced four wire three phase with a two element meter which made similar assumptions about the line to neutral voltages.
The old meters would run backwards when power was unintentionally exported.
The electronic revenue meters are able to accurately meter and record both positive and negative power on each line.
The default setting on many electronic meters is to sum the positive energy register with the negative energy register.
If you unintentionally export power you will be charged for the power that you export as well as for the power that you import.
racook; Many inverters have a provision to run a synchronizing signal so that they may be used in parallel.
Bill
"Why not the best?"
Jimmy Carter
Its entirely possible to run multiple inverter units connected to the one site, they will all 'self synchronise' with whatever is connected to their terminals, and in the absence of any control arrangement, will run as hard as they can based on whatever the connected solar capacity is on the DC side.
If there's no restriction on export, this is exactly what happens. If, however, there is a restriction on exporting, then some means of coordinating the output in order to not exceed the export limits at some point of coupling is required. Most of the time either hard limit reverse power protection is used, or if possible, some sort of coordinating device can be used to control the inverter outputs. The coordinating device doesn't replace any utility requirements for reverse power though.
EDMS Australia
If none is specified, we may either end up conducting a distribution impact assessment or ensure not to export power and ensure controls are in place to prevent the inverters to regulate the voltage at the PCC.
Depending on where these PV systems relative to the dist. system and whether there are there are line drop compensators and/or reclosersin the line circuit where these PV systems are connected to. Without a cut-off limit established by dist. utility, the impact of the grid parallelled PV systems cannot be determined without further studies.
Hence, having not to export will greatly help.
This is also what I have in mind, as a follow up of the above post. The O/H line circuit where the 300 kW PV facility is interconnected to does not have an voltage regulating device or reclosers along the line. I am thinking that If the power flow does not reverse towards the source substation of the distribution utility and the flow goes towards the nearest load, I don not think its a big of a deal anyways for the distribution utility.
As long as the PV facility short circuit contribution and power flows (and voltages)are checked at the distribution utility to ensure that all equipment and performance characteristics (by simulations) are within specified limits...it should not be a problem. In such case, the distribution utility and facility owner should come to certain agreements.
Also, as long as the PV facility will have some form of sensing capability to detect the distribution utility line tripped or open-circuited (islanded) to allow the PV system to isolate itself from the distribution utility line, then it should not be a problem.
These are my thoughts after reading portions of the IEEE 1547-2003.
Comments?
Bill
"Why not the best?"
Jimmy Carter
Some locations are moving towards requiring inverters that are capable of providing voltage regulation. The proposed draft for the next revision of IEEE 1547 dramatically changes the requirements for inverters, including staying online for many frequency & voltage excursions as well as providing voltage regulation. Here is a link to an overview of the proposed changes:
https://class.ee.washington.edu/500/2016aut-e/16-1...
I will read it today and comment as needed later.
Regards...a star for you also by the way.