Single Size Aggregate as Backfill
Single Size Aggregate as Backfill
(OP)
Hello
as the subject suggests , i want to know what are the specifications for using single size as back-fill material under structure i.e. a building, Do we really need to compact it or not ,isn't washing it sufficient ??
a quotation would be really appreciated.
as the subject suggests , i want to know what are the specifications for using single size as back-fill material under structure i.e. a building, Do we really need to compact it or not ,isn't washing it sufficient ??
a quotation would be really appreciated.
RE: Single Size Aggregate as Backfill
He has all the virtues I dislike and none of the vices I admire. - Winston Churchill, Sir (1874-1965)
f-d
ípapß gordo ainÆt no madre flaca!
RE: Single Size Aggregate as Backfill
RE: Single Size Aggregate as Backfill
RE: Single Size Aggregate as Backfill
RE: Single Size Aggregate as Backfill
just to clarify ; its to be placed below S.O.G. above foundations , its deep though 4 meters (about 13 feet).
is there a quotation on the issue from ASTM ??
RE: Single Size Aggregate as Backfill
Dik
RE: Single Size Aggregate as Backfill
RE: Single Size Aggregate as Backfill
the back-filling is 4 meters not the excavations because the natural ground level is very low at that area , and a basement option has been declined.
The Consultant advised to to fill it as 20cm layers , but since the back-filling depth is very high , he agreed to 50cm layers, but with compaction.
now i don't believe it is needed since its clean gravel, i don't see how such material can cause settlement.is compaction really needed?
i've searched high and low for compaction of clean gravel in us codes , but didn't find anything , that's why i've turned to you guys ..
RE: Single Size Aggregate as Backfill
My first reaction is ... Self Compacting aggregate is a Fairy Tale.
When it works - Great, but the fable has now gained some strength.
When it doesn't - Sometimes great pain, usually now a Compaction Grouting repair.
I do not allow any more than 12" (1/3 m) of clean fill under Anything, unless specifically compacted and usually stabilized by confinement (see above for fabrics or within a solid container, like stiff soil or concrete).
My biggest problem has been the belief in the Self Compacting aggregate Fairy Tale by municipal and large organization (private & government) engineers, who write so much of the specifications.