Conduit Size for grounding electrode conductor

Conduit Size for grounding electrode conductor

Conduit Size for grounding electrode conductor

(OP)
In case the grounding electrode conductor will be installed in embedded conduit, is there any limitation on the filling ratio of the conduit?
knowing that the conductor within the conduit will be drawn and installed before casting concrete.

RE: Conduit Size for grounding electrode conductor

I hope that this is non-ferrous conduit.
The Canadian Electrical Code states that the overall area of the conductor may not exceed 53% of the internal area of the conduit.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Conduit Size for grounding electrode conductor

The conduit fill requirements still apply. Like Waross said make sure using non-ferrous conduit or cut slits in where the conduit enters the enclosure, etc.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources