PMU for Event Analysis

PMU for Event Analysis

PMU for Event Analysis

(OP)
Most microprocessor relays are capable of sampling at rates of 128 samples per cycle or more. Would it ever be possible to get this type of resolution with Phasor Measurement Units or will these always be more for longer duration event analysis such as power swings and such?

The highest sample rate is currently 60 samples per second.

Thanks

RE: PMU for Event Analysis

I've heard rumors of 120 sample per second PMU data, but as a continuous stream of data there's no reason to have more. High speed recording should be limited to interesting bits of time or all you'll ever see is the hay-stack and no clue about the needles. High speed recording of very slowing changing things doesn't seem to be worth the data storage requirements.

RE: PMU for Event Analysis

There is a difference between PMU sample rate, which can be up to 48 samples per cycle (2880 samples per second), and PMU data rate for archiving and transmission, which I've also heard may be up to 120 samples per second these days. Obviously, downsampling occurs.

xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of Eng-Tips.

RE: PMU for Event Analysis

(OP)
OK, I think that's where I'm confused. I wasn't sure if the 60 samples/second was a sample rate or a rate at which data blocks (with multiple samples within) were sent.

RE: PMU for Event Analysis

The PMU data coming out of the relay is derived from the same data stream as the protection data, many times per cycle. A "slow" relay would be running at 960 samples per second; that's way too much data for anything you'd do with PMU data. For the fault event files, that data is continuously going into a buffer and if an event is triggered a block of data is stored in memory. The newer relays relays may be sampling at 8kHz or higher and allow the option to save event files with fewer points, perhaps 1, 2, 4, or 8kHz so that more and/or longer events can be held in the relay's memory before they begin to be overwritten. I'm aware of at least one relay that samples at 1Mhz, data from that one that hasn't been significantly down-sampled is drinking from a fire hose.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources