Maximum Concrete Volume Cast Limit
Maximum Concrete Volume Cast Limit
(OP)
Dear Eng-Tips Members,
I would like to know if there is any limit on Maximum Volume of concrete that can be cast in one go?
Other than providing construction/Contraction/Control joints in hot weather, are there any other specification that limit maximum volume of concrete cast in one batch ?
Reference would be appreciated.
I would like to know if there is any limit on Maximum Volume of concrete that can be cast in one go?
Other than providing construction/Contraction/Control joints in hot weather, are there any other specification that limit maximum volume of concrete cast in one batch ?
Reference would be appreciated.






RE: Maximum Concrete Volume Cast Limit
RE: Maximum Concrete Volume Cast Limit
Upto my knowledge, we cannot provide control/contraction joints in Raft.
RE: Maximum Concrete Volume Cast Limit
Dik
RE: Maximum Concrete Volume Cast Limit
RE: Maximum Concrete Volume Cast Limit
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Maximum Concrete Volume Cast Limit
Mass concrete concerns depend not only on the volume of concrete, but also the dimensions of the concrete. No matter how large the volume, if the raft is less than 3 feet thick, heat of hydration can probably be handled by common methods, such as chilled mix water or ice, placing concrete at night, etc.
www.SlideRuleEra.net
www.VacuumTubeEra.net
RE: Maximum Concrete Volume Cast Limit
In my case, contractor is pouring 1.4meter deep foundation raft and more than 10meter by 10meter in area in one go. He is not using any thermo-couples to control heat of hydration as he exclaim than there is no guidance regarding volume of concrete that can be casted without taking these measures.
@SlideRuleEra
Can you please indicate any reference for this 3ft thick ? as to justify it I need some technical document.
RE: Maximum Concrete Volume Cast Limit
Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies
RE: Maximum Concrete Volume Cast Limit
www.SlideRuleEra.net
www.VacuumTubeEra.net
RE: Maximum Concrete Volume Cast Limit
PCA Library Online Catalog
RE: Maximum Concrete Volume Cast Limit
I apologize that I havent mentioned correctly. Actually there are number of these and daily contractor is casting 5000-8000 cu.m without taking any measure to control Heat of Hydration.
@SlideRuleEra / EDub24
Thanks alot for sharing the references.
Just want to add. Is there any specific value I can calculate by doing any analysis that can depict the volume of concrete that is suitable to cast in one go?.
Thanks again everyone.