Cable tray passing through Battery Room
(OP)
What is the type of cable tray to be used, when it is passing through Battery Room? Does NEC specify the type of cable tray/conduit to be used in battery room?






RE: Cable tray passing through Battery Room
(A)Types NM, NMC, and NMS. Types NM, NMC, and NMS cables shall not be permitted as follows:
(7) In storage battery rooms