Slab-on-grade crack
Slab-on-grade crack
See attached slab layout, photo, and mix. The crack is approximately 75 ft long.
1. A 1.5 to 1.0 slab panel ratio per ACI is approximately met for the control joint layout.
2. 3 times the slab thickness in feet was used (this is a 5" slab) per ACI so the max spacing is 15 ft for control joints.
3. 6X6-W5.5xw5.5 WWR at 1.5" below the top of the slab was called for but not counted on for crack control. The WWR most likely pulled up during pouring.
4. Vapor retarder is directly under the slab.
There is an identical control joint layout North of the area shown that did not crack and the crack stopped as shown on the right side of the CMU wall as the same control joint pattern continued on the left side of the wall. I have a couple of ideas but I wanted to get other opinions on the crack formation.
RE: Slab-on-grade crack
Dik
Dik
Dik
Oh we are a silly bunch.
Dik
Not a through joint... just a slab 'weakening' to cause the cracking to occur. Aggregate interlock generally provides for shear between concrete panels. It has to be done at the right time.
Dik