Multi cable transit (MCT) system
Multi cable transit (MCT) system
(OP)
Does NEC/Saudi Aramco permits the passing of both the power and control/Instrumentation cables through the same MCT?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Multi cable transit (MCT) system
|
RE: Multi cable transit (MCT) system
Keith Cress
kcress - http://www.flaminsystems.com
RE: Multi cable transit (MCT) system
" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
RE: Multi cable transit (MCT) system
NEC permits cable of 1000 V or less to occupy the same cable raceway if the insulation is the same.[see art.300.3] So control cable could occupy the same raceway with power cables[usually]. Instrument cable only as permitted on 725 and 727 articles. See-for instance:
https://www.hawke-hts.com/en/technical-information...
http://www.emersonindustrial.com/en-US/egselectric...