Connecting 240mm2 cable to 160A circuit breaker
Connecting 240mm2 cable to 160A circuit breaker
(OP)
Hi,
A 3 phase cable with 240 mm2 cross section for each of the phases is required to connect to a 160 A circuit breaker.
The cable is too large (2.2 x the cross section of AWG 0000 (4/0)), and the terminals on the circuit breaker do not fit.
What accessories would be a good 100% legit (not ad-hoc fix) to make this connection?
A 3 phase cable with 240 mm2 cross section for each of the phases is required to connect to a 160 A circuit breaker.
The cable is too large (2.2 x the cross section of AWG 0000 (4/0)), and the terminals on the circuit breaker do not fit.
What accessories would be a good 100% legit (not ad-hoc fix) to make this connection?






RE: Connecting 240mm2 cable to 160A circuit breaker
RE: Connecting 240mm2 cable to 160A circuit breaker
http://ecat.burndy.com/Comergent/burndy/documentat...
section C148 adapter Y3428R From 500 mcm to 4/0
RE: Connecting 240mm2 cable to 160A circuit breaker