ASCE 7 Modal Response Spectrum Analysis: Scale Spectrum or Results
In reviewing ASCE 7-10 12.9, I see two possible ways to complete a MSRA.
Procedure A:
1. Run MSRA based on full design response spectrum
2. Scale results for R/I.
3. Scale up results for 0.85 of ELF if required by 12.9.4.2
Procedure B:
1. Scale design response spectrum for R/I.
2. Run MSRA based on elastic design response spectrum
Are both of these ways permissible? Would they theoretically yield same results?
RE: ASCE 7 Modal Response Spectrum Analysis: Scale Spectrum or Results
For a linear analysis they will both yield the same result. And, MRSA is always a linear type of analysis.
Thanks Josh, glad you responded, I am RISA user and understood one flow path but am reviewing calculations from SAP user which appears to be doing it differently and was trying follow along.