MED Voltage Motor - Rotor amps
MED Voltage Motor - Rotor amps
(OP)
Hi Eng-Tips
looking for some help on MV Motor, the nameplate gives the following information
2900Kw, 991 Rpm, 11000 V Y, 991 rpm, 50 hz .085 cos, Rotor 1375 A
This motor has been working fine for 15 + years I'm told, I have only started working in this plant.
In the last 2 years, the motor has started burning brushes on one phase and not always been the same phase.
We looked at the trends and the motor seems to be working at 80% of its capacity, but the rotor amps is very low just 70-80 amps per phase. We do see one phase with approx 10-15% higher reading tot he others.
On this trend we also see the vibration rises from normal 1.2 m/s to 2.6-2.9 m/s which is still quite low. The motor will then trip and the brush will be burned out.
I would like to try and ask your opinion as to why you think the rotor amps are so low and to see why you think the brushes are burning.
Regards
F.E.G
looking for some help on MV Motor, the nameplate gives the following information
2900Kw, 991 Rpm, 11000 V Y, 991 rpm, 50 hz .085 cos, Rotor 1375 A
This motor has been working fine for 15 + years I'm told, I have only started working in this plant.
In the last 2 years, the motor has started burning brushes on one phase and not always been the same phase.
We looked at the trends and the motor seems to be working at 80% of its capacity, but the rotor amps is very low just 70-80 amps per phase. We do see one phase with approx 10-15% higher reading tot he others.
On this trend we also see the vibration rises from normal 1.2 m/s to 2.6-2.9 m/s which is still quite low. The motor will then trip and the brush will be burned out.
I would like to try and ask your opinion as to why you think the rotor amps are so low and to see why you think the brushes are burning.
Regards
F.E.G





RE: MED Voltage Motor - Rotor amps
RE: MED Voltage Motor - Rotor amps
It might also be time to consider dragging this into the modern age, because generally large motors like this are intimately tied to the bottom line of whatever your company does, so having it operate reliably means everyone stays employed. If your operating speed never changes now, consider using a solid state soft starter for the stator and that fixed resistance value you already have. If the speed needs to vary to follow some sort of process signal, you can use a VFD but at 11kV that's going to be a budget buster.
" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
RE: MED Voltage Motor - Rotor amps
the slip rings would likely be in less than optimum condition. Including the brush holders.
Photographs of the slip rings, brush holders and the failed brushes provide very useful details.
John
RE: MED Voltage Motor - Rotor amps
Thanks for initial replies.
This motor has been working since Jan 2000, its a slip ring motor started by the same liquid resistance starter and the sequence of starting has not changed over the years. Its a fixed speed all the time. its starts very infrequently, it runs normally for weeks/months at a time.
I have attached some photos, one attachment shows the damage after failure, the other show's the motor in operation with one brush wearing more than the rest, the brushes were changed after this was found.
The slip ring assembly was repaired, skimmed with new brushes fitted and returned to service within 3 months it had the same failure.
F.E.G
RE: MED Voltage Motor - Rotor amps
Are you using the brush grade recommended by the OEM?
Muthu
www.edison.co.in
RE: MED Voltage Motor - Rotor amps
we recently fitted CT's to measure the motor amps, the OEM no longer supplies the brushes for this motor but we are using the same grade brush as the original and they have been working well up to this problem.
F.E.G
RE: MED Voltage Motor - Rotor amps
between the right and center brush sets. Note the discolored (darker) insulators.
There is also a sign of intense heat along the edge of where the slip ring is mated with its insulating hub.
Note the dull look of the metal spacing rod and its lost varnished sheen in comparison to the exposed
portion of the rod further to the left.
You’re not going to want to read this.
The entire slip ring assembly pressed on the rotor shaft must be removed from the apparatus
and completely cleaned/washed, dried out and re-varnished, or totally replaced.
Obviously the brush holder assembly would need the insulators replaced, or inspected for
their electrical integrity as well.
As clean as it looks, it’s difficult to comprehend potential tracking between the
three rings, “but” it does… and likely is.
One opinion based on one photograph.
Keep us posted.
John
RE: MED Voltage Motor - Rotor amps
And the very low rotor amps running is trying to tell us something
Excessive wear on those brushes
Could there be something wrong with the liquid resistor, I am not familiar with the liquid type.
RE: MED Voltage Motor - Rotor amps
RE: MED Voltage Motor - Rotor amps
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: MED Voltage Motor - Rotor amps
You use CT's on the rotor circuit? Your read rotor currents are then suspect.
Possible reasons for brush wear out.
1. Wrong grade
2. Inappropriate spring pressure
3. Loose connection from slipring to rotor winding lead
4. Hard dirt (like cement particles)
5. Excessive temperatures
Have you tried measuring the brush temperatures during running with a thermal camera or a non-contact temperature meter?
Muthu
www.edison.co.in
RE: MED Voltage Motor - Rotor amps
I used six 60 gallon plastic barrels and 12 truck leaf springs for electrodes. With a clamp meter on the lead, I poured salt into the water until I saw an acceptable current. I was running about 200 Amps per barrel, 400 Amps per phase.
What's the point of this?
I boiled off about 600 Gallons per day of water. I made multiple trips to the site every day to refill the barrels.
In the mornings the barrels would be close to empty.
Please tell me that you are not leaving the liquid rheostat in the circuit while the motor is running at speed.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: MED Voltage Motor - Rotor amps
I would suspect the quality of your brushes has changed.
RE: MED Voltage Motor - Rotor amps
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: MED Voltage Motor - Rotor amps
The Elec guys tell me they checked that the contractors are working properly and the starter is out of the system when the motor is up to speed.
I'm a mech guy so I would like to clarify the following, I would have thought that when the motor is up to speed there would be no volts/amps in the rotor is this right ? We are seeing approx 70 amps with the CTs which we only fitted recently, as they only ever trended the stator amps prior to the problems. What we are doing now is monitoring it with the CTs and when it gets to 250 amps it trips, this is actually protecting the motor now and we know this as we have had 8 months now trouble free but we have had 3 trips which is a problem for us. The 250amps was just a guess in case you wonder where we came up with that.
They fitted rope type CTs from Powertekuk RCTRMS-3ph/1500/4/500 (4-20 mA)
Edison, we got a thermal check done and it's shows one phase a lot hotter than the others I just don't have it to hand as I'm away from site. The area is clear with no deposits of dirt, the grade of the brush is the same as the OEM according to SCHUNK and new brushes and springs were fitted after failure.
Thanks for input so far guys
RE: MED Voltage Motor - Rotor amps
Good point, the CTs won't measure the slip frequency I missed that.
Is there a correct way of doing that?
I recall we had a clipon that was nothing more than a magnetic circuit with a changeable moving iron movement, Hall effect nowdays I guess.
RE: MED Voltage Motor - Rotor amps
"Please tell me that you are not leaving the liquid rheostat in the circuit while the motor is running at speed."
Once the LRS is shorted (either via contactors or a shorting ring at the end of the travel of the LRS), not much current will be flowing through the liquid. The case you are describing is where the salt water was used as a load 24x7.
Feg
"I would have thought that when the motor is up to speed there would be no volts/amps in the rotor is this right"
No, the rotor will have the rated rotor current at full load at the rated speed.
Again, you cannot use CT's to measure low frequency rotor currents. And rotor currents are not measured or used for motor protection in normal applications.
A complete revamp of your sliprings (not just surface machining) is needed.
Muthu
www.edison.co.in
RE: MED Voltage Motor - Rotor amps
exhibits during its curing process (which takes years).
The photo of the slip ring area of the motor clearly shows one phase is affected. Not all three.
(Silicone -out gasses- would not choose just one phase; it would attack all copper bearing surfaces.)
The slip ring area of the motor is tracking “potential” which needs to be corrected.
And the only way that can happen is by removing the apparatus from service, and fixing it.
The absence of visual dirt or debris is meaningless. Conducting carbon from past brush changes can be/is likely
painted over from previous attention to the apparatus.
John
RE: MED Voltage Motor - Rotor amps
Easy approximations for the rotor of a slip ring motor.
- current is proportional to load
- voltage is inversely proportional to synchronous speed.
- frequency is inversely proportional to synchronous speed.
So, at full speed and full load you should see a low rotor frequency, a low rotor voltage and rated rotor current.
RE: MED Voltage Motor - Rotor amps
1.2 m/sec would be very high vibration velocity. I assume you meant 1.2 mm/sec.
=====================================
(2B)+(2B)' ?
RE: MED Voltage Motor - Rotor amps
the vibration was a typo its 1.2mm sec
F.E.G
RE: MED Voltage Motor - Rotor amps
Are the contacts in the shorting contacter in good condition?
Have you considered a ductor test of the rotor to determine if there is a failing internal connection to one slip ring?
A poor connection to the slip ring may cause excess heating of the slip ring under heavy loads.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: MED Voltage Motor - Rotor amps
=====================================
(2B)+(2B)' ?
RE: MED Voltage Motor - Rotor amps
RE: MED Voltage Motor - Rotor amps
In case if we replace some worn brushes with grade other than original. Suppose new brushes have high conductivity comparing to original brushes, then these new brushes will carry more current than other brushes. Wear rate will increase on these brushes due to excessive current and finally in very short time brushes will reach to their minimum length. Now at this moment, burden of those worn brushes will be shifted to remaining brushes and current density on remaining brushes will increased. In result, after some period all brushes would be looked heated-up and consequently worn-out.
2: I think your current measurement seems not ok; you cannot use normal CT's to measure low frequency rotor currents.
RE: MED Voltage Motor - Rotor amps
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: MED Voltage Motor - Rotor amps
2. Those worn brushes are found in a different phase each time.
3. But (at least from latest photo), the two brushes within a given phase have similar wear?
4. After the failure, brushes replaced but nothing done to slip ring?
If I have it right that's tough to figure.
Overheating may be a consequence of severe brush wear which extends spring to the point that contact pressure is lost and it creates the heat. But in that case, what would cause the severe brush wear to begin with.
Items 2 and 3 don't seem very consistent with a mechanical cause.
Electrical cause on rotor doesn't seem likely to shift phase.
Maybe something to do with external shorting...if there are multiple contacts involved and all of them have some erratic behavior. Just a shot in the dark, not sure. Maybe try some resistance measurements from the brushes with brushes lifted off the slip rings and the external circuit in the shorted/running configuration (with motor not running though!).
Photos of slip rings or the other side of the brushes might possibly have some clues.
Also if there is a spectrum associated with this increased vib, analysis of which frequencies increase may give some clues (does it suggest a stator unbalance 2*LF or a rotor unbalance which I think might have pole pass characteristics, or something else). For that matter, any unusual frequencies in the normal vib? Also if you notice the vib going up you may be able to grab some three phase current measurements on stator or rotor if there are safely accessible measurement points and methods. Also take a close look at your maintenance procedures, spring tension checks, condition of slip rings, also the potential contamination issues mentioned by John / D'Arsonval
=====================================
(2B)+(2B)' ?
RE: MED Voltage Motor - Rotor amps
Wouldn't imbalanced current on the three rotor poles cause vibration?
Higher current on one pole is caused by lower resistance in that pole. Lower resistance could be due to:
Shorted turns in a winding?
Shorter lead length to the shorting point?
Higher brush contact pressure compared to the other poles?
I've heard that brushes have a negative coefficient of resistivity within certain temperature ranges (a property of carbon). Something I've been wondering: to avoid thermal runaway, is it necessary to have a certain minimum resistance in the shorting circuit on each pole such that the resistance of the brush is not a significant portion of the total resistance in each pole? (i.e. varying brush resistance does not significantly influence rotor current) If the shorting resistance in each pole was approximately equal but more importantly, too small, would thermal runaway be possible? In such a case, I would expect the pole to burn out to be the one that had the lowest contact resistance which is I'd guess would be most dominantly determined by the initial spring tension.
Is it typical that the brushes are in shorting circuit on a WRIM?
RE: MED Voltage Motor - Rotor amps
We give low voltage * 3 x 380 Volts* on stator windings ant then simulate motor start with contactor and timers beetween every steps .
Then you should measure current on every stator and rotor phase with amper clamps without big risk because motor did not run .
In several last steps, stator and rotor currents are a bit larger so that you need to pay attention to this when selecting the power wire .
IF is current at every step of all phases is same and ballansed you did not have problem with rotor , contactors , start resistor and your problem is on the other side .
Good luck
RE: MED Voltage Motor - Rotor amps
The rotor will turn even at 380 V if the rotor circuit is closed with or without resistor.
Muthu
www.edison.co.in
RE: MED Voltage Motor - Rotor amps
Uncoupled the rotor will turn.
We don't know what this motor or the motor that panter tested were driving.
A lot of loads will not turn with 3.5% of rated voltage applied.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: MED Voltage Motor - Rotor amps
It is coupled with pump and 380 V is low voltage to turn rotor during test .
Good luck !
RE: MED Voltage Motor - Rotor amps
Have you checked the incoming supply for balanced phase to phase voltages.
Check first with the motor off-line and again with the motor running.
A running induction motor acts as an induction generator and will try to correct unbalances in the supply.
This may cause circulating currents and excess rotor heating.
My experience with unbalance issues has been with squirrel cage motors, synchronous alternators and transformer banks.
Given that unbalanced loading has caused rotor heating and damage in alternators, and unbalances have caused unbalanced currents in motors and rotor heating and in the case of transformer banks, caused one transformer to run much hotter than the second overheated transformer, it is possible that unbalanced supply voltages may cause heavier current in one brush.
Bill
--------------------