Obtaining centre of rigidity in Etabs
CSI knowledge Base tells This:
""During analysis, ETABS automatically calculates this coordinate for each floor diaphragm. The diaphragm assignment must be present in the model. Center of rigidity and center of mass are then displayed by selecting Display > Show Tables > Analysis > Results > Structural Results > Centers of Mass and Rigidity > OK""
But the option 'Centers of Mass and Rigidity' is not there inside 'Structural Results' in Etabs.
Please help me on this..
Ravi K
RE: Obtaining centre of rigidity in Etabs
Do you have your diaphragms set to 'rigid'?
Forgotten to set the diaphragm rigid. Now it is showing the option 'Centers of Mass and Rigidity.
Thanks..
How can we increase the eccentricity in the model ?
if eccentricity = 1.5*structural + 5% accidental.
Go to Analyze > Set Load Cases To Run
Is "Calculate Diaphragm Centers of Rigidity" checked?
Yes i did it @DETstru,
You can manually adjust the eccentricity of each floor in the Response Spectrum Load Case Data.
That's under Define > Load Cases
(I'm assuming you're running a response spectrum case)
@DETstru
No, I am not running a response spectrum case. I am only applying lateral load calculated by seismic coefficient method at the frame joints. I wanted to increase the eccentricity value for safer design. But i could not find the the option in Etabs.
If you are referring to user loads you may find the eccentricity field on your bottom right corner when you hit modify load pattern
If you meant code static loads it should be on the top left corner