CEC Section 8-104 Max Circuit Loading vs Table 12E (DLO ampacity) in lieu of Table 1
In Canadian Electrical Code- does 8-104(4)(b) [8-104(d) reads: With 100% rated circuit breaker, 85% of the rating of the circuit where the ampacity of the conductors is based on Column 2, 3, or 4 of Table 1 or 3] still apply if we're sizing DLO cable based on Table 12E [Allowable ampacities for DLO cables in a permanent installation]?
To me, Table 12E is equivalent to Table 1 with the exception that Table 12E has different sizes for the larger DLO cables (535kcmil rather than 500kcmil etc). I would figure 8-104(4)(b) would also say "circuit is 85% of the rating of conductors based on Table 1, 3, or 12E...but it doesnt.
Do we need to include an additional derate for 85% circuit rating? Code does not explicitly say 85% of ampacity based on 12E.
RE: CEC Section 8-104 Max Circuit Loading vs Table 12E (DLO ampacity) in lieu of Table 1
I would compare the temperature rating of the DLO cable with the temperature ratings for columns 2,3,or 4.
Match the temperature rating and use that column to determine derating.
Bill
"Why not the best?"
Jimmy Carter