ELECTRICAL DB ENCLOSURE

ELECTRICAL DB ENCLOSURE

(OP)
Hello guys,

are there electrical control panels which are 2 hrs fire rated? we need to have them due to fire strategy,

or can we use the normal control panel and enclose it in a 2 hrs fire rated material and what is it?

please assist with contacts of suppliers

cheers

RE: ELECTRICAL DB ENCLOSURE

They are probably fire rated but it may be difficult to acquire the documentation.
We had a similar issue with drop-in lighting fixtures. Eventually the manufacturer confirmed that all drop in fixtures have the same rating as regular suspended ceiling tiles.
Try calling the manufacturer.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: ELECTRICAL DB ENCLOSURE

But also consider that it's doubtful that anything you put into an electrical enclosure will survive for 2 hours operating in more than 40-50C internal temperature. So yes, the enclosure may survive but nothing inside can be guaranteed to function afterward. I don't even think the Fire Pump Controllers are rated for being IN a fire for 2 hours.


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close