API 650 Circulation Vents

API 650 Circulation Vents

API 650 Circulation Vents

(OP)
thread1452-317354: Circulation vent design- API 650 Internal Floating Roof Storage Tank

Hello, I have a copy of this standard and was not clear on if it should be applied to fixed roof tanks as well with regards to the circulation vent requirements. I have several fixed roof tanks on site that have these vents. The fabrication drawings reference API 650 as the construction standard.

Are these vent requirements applicable to fixed roof tanks?

Thank you,

RE: API 650 Circulation Vents

Circulation vents in Annex H are only needed for internal floating roof tanks. Fixed roof tanks without an internal floating roof do not need and should not have circulation vents - they should have PV and emergency vents.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources