supporting 200lbs on center of a 14' span.
I am trying to support 200lb duct on a 14' span. I would prefer to use angle, but am not opposed to channel if it's necessary. My gut tells me 4x4x1/4 is safe, maybe 3x3x1/4. i would like to use beam clamps on the edge of the horizontal leg, but can drill closer to the vertical leg if i gain some capacity by reducing torsion. any help is much appreciated. thank you in advance.
RE: supporting 200lbs on center of a 14' span.
I have some tables that cover laterally unsupported angles......and for 14', they both show that L4x4x1/4 & L3x3x1/4 as being ok for flexural loads (i.e. the load you called out; A36 steel used). By the way, that doesn't include a deflection check.
However these tables don't check torsion (shear) stresses or rotation. So that would be an additional check that would need to be done.
I'd just check the flexural capacity of the section at max moment (PL/4) and deflection. You could always use a double angle (two smaller angles 1 1/2" X 1 1 1/2" leg to leg) if you are worried about torsion