Pressure regulating valve
Hi gentlemen, I'm new to this forum!
I have a question regarding a PRV. There is an existing line of pressurised air that is planned to be divided at one user point into two. One branch will be reducing pressure to 2, and another should stay at 6. Now, is there a PRV, that will be pre-set to reduce the bar from 6 to 2 and lock, but also have a possibility to be manually closed from 2 to 0? At the end of the day, operator should be able to come up and close the valve, shutting down the process.
Maybe there is some sort of a PICV that could do that?
Thanks in advance!
If pictures of the process are needed, I may be able to provide them for further help.
Cheers!
Thanks in advance!
Cheers!
RE: Pressure regulating valve
BTW PRV is often confused for Pressure Relief Valve so much better to use full words sometimes to avoid confusion.
But, out of curiosity - is there a valve, that can do a two-step job like I described? I've seen a similar setup in a Quality Lab, where they didn't want to see 6 bar, so on the inlet, there indeed was 6 bar, reduced down to 2 bar with further hand-adjustment possible (hand dial) between 0-2 bar downstream.
I may be wrong and they just had a block containing two valves, but if I'm not imagining it - could someone shed some light on that idea?
Regards and thank you LittleInch!
There are many many regulators on the market so you will find one to meet your requirements.
So this mysterious PICV that entails both isolation and pressure regulating jobs isn't desirable if shutdown (i.e closing of the valve) is done frequently?
I also wonder if my P&ID show PICVs as Pressure Indicator Control Valve or Pressure Independent Control Valve... confusion.
Thanks, LittleInch!
PICV to me would be Pressure INDICATING Control Valve, i.e. it has pressure gauges on it....
- No throttle valve (especially the very expensive ones, their extra cost comes from precisely matching a flow profile at near-zero flow and maximum flow) can ever be relied upon for bubble-tight seal. They just are not designed for it. The seats are designed to allow flow even when very nearly closed, that design will rarely be consistent with zero flow. If one happens to give you a bubble-tight seal once, you have no assurance that it will repeat that performance the very next time it goes to shut.
- You do not want your operators adjusting the regulator to zero and then back to target pressure, the cost in labor will rapidly exceed the cost of a block valve.
Expecting a regulator to shut off flow will always be a false economy.David Simpson, PE
MuleShoe Engineering
In questions of science, the authority of a thousand is not worth the humble reasoning of a single individual. Galileo Galilei, Italian Physicist
I attached a part of the process. Yellow line is kept at 6 bar (supplying line is already at 6 bar, but fluctuating, so PRV to maintain preset pressure with possibility of regulating between 6 and 2). And the blue branch (proposed tie-in) to be kept at 2 bar with possibility of reducing to 0. What's bubbled is a proposed branch, but I don't see why they want to tie-in so far upstream. We could easily soft-connect the tie-in at the flange in UL-51697 (inside the room, where two air drops are required).
Thoughts, gentlemen? I think valve question has been answered. Manual floating ball valve before the PRV with an indicator.
The P&ID just looks fine to me except that the second PCV set at 0-2 bar need to be a manual one instead of self-regulating. In my experience a self- regulating valve can't regulate to 0 bar. If the designer, don't have a symbol for manual PCV, they should specify 'Manual' at the bottom of the valve.
The P&ID is not a dimentional drawing. You need to see the Isometrics to figure out how far the tie-in is outside the building.
Ganga D. Deka, P. Eng
Canada