Opinion - LTB with Stiffener Plate
I've got a project where a big I-beam is required. I routinely try to frame secondary framing into the web of the primary I-beams to reduce the unbraced length of the beam. But I've got an issue where the depths are not close. A W27x84 and smaller "joists" - W16x26. I don't want to increase the beam size any more than I have to....it is spanning 59 feet and I need to find a way to reduce the unbraced length. I don't think the architect will go for kickers from the bottom flange. I would appreciate thoughts on the idea attached.
RE: Opinion - LTB with Stiffener Plate
1) Old school wisdom was that a connection covering 60% of the girder depth was sufficient for rotational bracing. You're about there. I think that there's a real rule somewhere in AISC now but I can't recall what/where.
2) Do you not have a diaphragm on top of the beams that restrains their movement in the plane of the diaphragm? If you do and compression is limited to the girder top flange, then all you need is nodal bracing of the top flange and infill beam depth is of no consequence.
3) Worse come to worse, I think that your proposal would be quite effective.
The W16's would routinely be considered as laterally bracing the top flange if it was in compression - assuming that there is a diaphragm or other means of securing the W16's against lateral movement as well.
With a negative moment condition, the stiffeners could indeed be considered as bracing the girders bottom compression flange assuming there is a rigidity between the W16's and the stiffeners.
AISC has requirements for the minimum stiffness required - in your case you are using the flexural stiffness of the W16's (and to some extent the plates) to keep the girder braced.
If it is a roof beam, do you have any net wind uplift? (D+W) Something to check also to verify that there isn't any negative moment in the girder.