Fiber Optic Cable Service Loop
Is there a Code Requirement to leave service loops for Fiber Optic Cable? I have heard and read lengths of anywhere from 10' to 100' but I do not see anything in the NEC that explicitly says that a service loop of any length is required. Does anyone know of one?
RE: Fiber Optic Cable Service Loop
(A) Conductive and Nonconductive Cables. Unlisted conduc‐
tive and nonconductive outside plant optical fiber cables shall
be permitted to be installed in building spaces, other than
risers, ducts used for environmental air, plenums used for envi‐
ronmental air, and other spaces used for environmental air,
where the length of the cable within the building, measured
from its point of entrance, does not exceed 15 m (50 ft) and
the cable enters the building from the outside and is termina‐
ted in an enclosure.
The point of entrance shall be permitted to be extended
from the penetration of the external wall or floor slab by
continuously enclosing the entrance optical fiber cables in
rigid metal conduit (RMC) or intermediate metal conduit
(IMC) to the point of emergence.