Live load v.s. moving equipment load

Live load v.s. moving equipment load

(OP)
I had this discussion in office and I appreciate if someone educate me or clear the mud for me.
I had posted a day ago a question on manlift load check on a floor plate and I want to here state that my intention is not duplicating the question but is somehow related.

I been asked if it is okay to place a manlift on 17 floor of an open steel structure floor which the floor is checker plates. The original drawings state that parts of the floor load is 100 psf and parts 500 psf rated. Some mechanical engineer colleague tell me that the 3' by 8' 5500lbs manlift is okay to be rolled on the floor.

I told them I don't think that floor rating includes the manlift/moving load and I have to use the tire width, pressure and graphs in a book that I forgot the name of it and apply point loads and check regardless the floor rating.

Am I correct? or this wheeled manlift can be consider as the 500 psf rated load?

I appreciate using a simple language I understand.

Respectfully,
Your colleague

RE: Live load v.s. moving equipment load

Heavy industrial live load is 250 psf or 3,000 lb. The smallest forklifts have 3,500 lb wheel loads. If the floor cannot support the load, it should not be rated for 500 psf because it implies that it is the area of floor that should be used for this purpose.

I would check it with a single plate FEM with a pressure tire load, and roughly estimate effective widths and the average maximum stress across the effective width (not the max stress).

It's extremely odd that you have an open steel structure with checkered floor plates. That seems like a water/corrosion/slip hazard.

RE: Live load v.s. moving equipment load

I agree with your approach; the plate has to be evaluated based upon contact area.

RE: Live load v.s. moving equipment load

As BB noted... your approach is sound... the lift can likely be supported without issue on the 500 psf area, but, unlikely on the 100 psf area... should, however, check out both conditions.

Dik

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close