Mis-placed anchor rods

(OP)
If anchor rods are mis-placed by inches, can post installed anchors be installed adjacent to the cut off anchors?
My thought is that the cut off anchors would be like a piece of rebar in the footing.
I should say that there is tension on the new post installed anchors.
The cut off anchors would be within the potential failure cone of the new anchors.

RE: Mis-placed anchor rods

I'll buy that. KootK approved.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Mis-placed anchor rods

The only possible difference I can think of is if you're literally tangent to the other anchor you'd have a bit of epoxy trying to bond to the old anchor. I can't imagine that has any meaningful impact to the tension capacity (for better or worse).

And if the breakout cone cuts through the old anchor it's like added shear reinforcement!

RE: Mis-placed anchor rods

Quote:

If anchor rods are mis-placed by inches, can post installed anchors be installed adjacent to the cut off anchors?
My thought is that the cut off anchors would be like a piece of rebar in the footing.

Yes but they wouldn't have the same effect as re-bar would. (If you are thinking about the cut off anchors as providing some sort of reinforcement for the anchor zone.) Depending on the diameter of the bolts, having cut off anchors a few inches away shouldn't have much of an impact on the post-installed anchors. Too close and you could impact the bond......but (say) 1/2" diameter post-installed anchor 2-3 inches away from a cut off 1/2" diameter bolt? It's like the cut off isn't even there.

RE: Mis-placed anchor rods

(OP)
1" rods cut off
new 1" post installed anchors 2" away
center to center distances

RE: Mis-placed anchor rods

The main article does not deal with your issue, but someone asked about it in the comments. Simpson responded take a look. Simpson SE Blog

RE: Mis-placed anchor rods

Quote:

1" rods cut off
new 1" post installed anchors 2" away
center to center distances

Given that, I'd take a bit of a reduction. How much would be a judgement call about the amount of failure zone/bond interrupted by the adjacent bolt. sandman21's article provides some good info.

RE: Mis-placed anchor rods

Hilti put out some literature regarding holes, drilled in the wrong location or started but unable to reach proper depths and therefore abandoned, and their effect on anchors installed adjacent to the abandoned holes. I'll try and find the stuff but I would likely consider it something akin to that.

RE: Mis-placed anchor rods

A local Hilti rep stopped by our office today and had us answer some survey questions. One of the questions was regarding how often we used post-installed anchors to replace mislocated cast-in-place anchor bolts. Seems it's an issue they've been looking at. I would give them a call because they are always helpful and have great technical as well as anecdotal knowledge.

RE: Mis-placed anchor rods

As it turns out, it was actually a Simpson Strong-tie engineering letter regarding abandoned holes. It is just a formal presentation of the info in the link sandman21 provided.

RE: Mis-placed anchor rods

(OP)
I have been in touch with Hilti rep.

RE: Mis-placed anchor rods

Care to share what they told you?

RE: Mis-placed anchor rods

(OP)
Hilti rep referenced some testing done in the 80's [no link provided] with abandoned holes and wedge anchors.
The response did not address my specific situation with an abandoned cast in anchor.
I am waiting on additional information.

RE: Mis-placed anchor rods

@ the OP: I sketched out a variety of failure/bond zones for your situation and I came out with about 8-15% reduction in capacity. (Just thought I'd share.) That's not that far off from some of the numbers in that Simpson's blog.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close