House's backwall as retention wall
4

House's backwall as retention wall

House's backwall as retention wall

(OP)
We are brainstorming for the client project. The lot has limited buildable land with a big hill in the back. The client wants to explore the option of cutting down the back hill which resulting in 20-25 ft wall.

One option is building the house with the 20ft concrete back wall flush against the cut hill and also act as retaining wall. Is pour concrete wall or ICF wall suitable for this purpose? Is soil nailing also required to stabilize the slope in addition to the concrete wall?


The other option would be shotcrete/ soil nailing retaining wall and 5 feet space between the wall and the back of the house. The house will be smaller and the wall will be higher, about 25 ft

In your opinion, which option would be more feasible and economical?

RE: House's backwall as retention wall

Before you make any decisions you need to know in detail what that hill consists of. The strength properties, water conditions,etc are essential for evaluating the current condition as well as predicting future conditions. It may take considerably more than sampling the exposed surfaces. I'd suggest involving a geotech engineer and making use of soil exploration and soil laboratory testing services.

RE: House's backwall as retention wall

Impossible for anyone to provide advice with out seeing any soil profile or topography of the slope

RE: House's backwall as retention wall

Agree that you need soil properties for a wall like that.

25ft is a pretty good sized cantilevered retaining wall. Walls can certainly be built that high, but there might be significant deflections at the top even if you design for in situ (ko) earth pressures versus active pressures (ka).

This is fine for a stand alone wall, but when there is a house attached to the wall, there might be issues with the movement.

RE: House's backwall as retention wall

(OP)
Thanks!

I don't have the detail report yet but the preliminary result show silty sand and sandstone/siltstone bedrock in the area for the house. The hill has 12 inches clay soil on surface but there is silty sand soil below, similar to the building site

The slope on the surface of the hill is about 25% grade.

RE: House's backwall as retention wall

Roughly where in USA or other country it so we can guess at geology as a start. Maybe some pointers can be offered. Any geology mapping available to you?

RE: House's backwall as retention wall

(OP)
High desert Southwest. Arid, 7-8 inches of rain per year.
I look up the geo map and this is the info

description OLDER ALLUVIAL DEPOSITS
unit type Lithostratigraphic Unit
lithology Unconsolidated, Coarse-detrital
geologic history Miocene to Quaternary

RE: House's backwall as retention wall

I'd want to see a typical SPT type test boring from a cut bench about 50-60 feet or so higher than the proposed wall footing run down to 10 feet or more below footing elevation, all dependent on slope. The steeper the slope the higher the start. Of course topography mapped also. The object would provide info for a slope stability evaluation. One boring may not be sufficient depending on what is found.

RE: House's backwall as retention wall

I would want to keep the retaining wall and the house separate. If it were a more substantial structure than a house, it might be feasible to use the building structure in resisting the embankment pressure, but not a house...

RE: House's backwall as retention wall

(OP)
How much is the typical cost for a shotcrete/soil nailing retaining wall of 20 ft height and 100ft width?

RE: House's backwall as retention wall

Before you get into any details, such as nailing, there may be the need to hold back a significant volume of soil that needs major facilities. These may be as significant as a major concrete wall held there by grouted in tied backs extending beyond a possible slip plane, perhaps 80 feet in. A stability evaluation is certainly needed to determine any such approach. With a sloping(hill) surface up hill from a "wall" the potential horizontal pressures can be significantly higher than for a level surface there.

RE: House's backwall as retention wall

(OP)
Thanks!

Assuming no complications, how much is the typical cost for a shotcrete/soil nailing retaining wall of 20 ft height and 100ft width?

RE: House's backwall as retention wall

OG again.

I am throwing out a thought that may or may not be taken up. Let's say the site hill up hill from the excavation has some form of "glue" or "temporary" adhesion that once disturbed results in a weaker shear strength test result. Thus any common sampling and testing method is likely to not show that added advantage. A common situation with partly saturated sand with temporary cohesion gives the same impression until dried. However,at the subject site the "glue" may be reasonably permanent and might not be taken advantage of with SPT estimates , etc..

I have run a few in-place direct shear tests that generally conform to ASTM-D4554.
Here is a link showing the test. http://file.yizimg.com/175706/2012051620512314.pdf



In my case I used a back-hoe with bucket resting on a support, as the resistance to push a calibrated hydraulic vertical jack against (proving ring). The horizontal push was supplied by a hand jacked hydraulic cylinder with calibrated pressure gauge to read the push being applied. This set-up has been used to get on-site shear characteristics for design of excavation bracing, waste product disposal pile stability, etc. It takes some time and field equipment, but I'd prefer it to any lab test.

One may have to run three or more separate set-ups since any "gluing" factor (if there is any) will be destroyed by each test run. For the sandstone I have experience with there is a form of glue holding the sand grains together, sometimes quite weak.

RE: House's backwall as retention wall

25ft is a big wall. I dont think you can soil nail and shotcrete in a silty sand. How can you cut the face vertical or near vertical, install soil nails and then shotcrete without the soil collpsing.

You need a top down construction method i think. A secant bored pile wall could be an option as this would be waterproof in the permanent condition. Drill the bored piles to depth and then excavate.

If you get a borehole on the slope and topo of the hill i would post it as you would get better responses. Someone may even do a prelim design for you if they are feeling generous.

RE: House's backwall as retention wall

(OP)
Thank you so your help and answers. I really appreciate it.
The hill was already partially excavated. There is an existing borrow pit there for more than 20 years. We hope to widening the pit and put the house there. The back-hoe cannot get to the top of the pit to sample because of the topography.

Here is the topography map with the house(red) and retaining wall (green)




Here are the photos of the actual pit and the wall





Thank you again for your help!

RE: House's backwall as retention wall

The topog and photos help. However for scale, what is the size of the house rectangle? More constrast in the topog map drawing would help.

My first reaction is that there is some cementing of the sand to allow a steep cut to stand, but it is not totally stable. It appears that between el. 765 and 790 a possible earlier much higher cut condition was present and since then some failing of that cut has occurred. Not a good sign.. The sloughed piles give the impression that what you see is result of deterioration of the earlier steep cut slopes.

A geotech would be able to tell more of what is there, but it appears to be highly weathered sandstone. If that is the case,any steep slope should be considered as not permanent and some day will erode and maybe fail with large volumes moving. Simple slope erosion resistance may not be sufficient here. Thus an experienced geotech would be mandatory on the job if it was me. Access to the slopes above the old pit it must be obtained so that a drill rig can do the boring there. If needed use a tractor mounted rig.

The direct shear test I described might well also provide good info about what is there. It could be run in a test pit at an elevation midway between top of final cut and floor grade, off to the side. The object would be to test the layers that also are behind the cut slope now there.

RE: House's backwall as retention wall

(OP)
Sorry for not including the scale. The red rectangle is about 60×80 feet

RE: House's backwall as retention wall

(OP)
What would be the option for the Retaining wall?

RE: House's backwall as retention wall

(OP)
BTW, the next door neighbor was already built and the site has similar elevation.



RE: House's backwall as retention wall

Your neighbor cut back the slope to a stable condition with a few small walls at the base. If you have to keep a near vertical wall, look at some of these photos with tied back walls. Simple soil nailing is not suitable for what it appears you want. One slope in your photos is about 32 degrees, typical angle of repose for some sands. Cutting back to that slope would work.

https://images.search.yahoo.com/yhs/search?p=tied+...

RE: House's backwall as retention wall

While you are "playing" with various options, assume excavating a stable cut slope at 33 degrees to the horizontal (not allowing for possible cementing that may help), you need land extending up the hill about 60 feet for that cut starting at elevation 765 for rear of rear level place (lawn???).. Buy land back about 80 or 90 feet to be sure to allow for future unknowns. Might be cheaper than a tied back wall. A geotech might be able to recommend a less costly alternative.

RE: House's backwall as retention wall

I second the 'buy more land' option.

Being serious, If that is at all a viable option; then it very well might be cheaper than the wall options you are looking at.

RE: House's backwall as retention wall

(OP)
What would be a rough estimated cost of these options?

Land is not a problem. The back of the lot is more than 200ft uphill from the wall. If cutting the slope down to 33 degrees, do we still need some sort of erosion control or surface cover? The exposed dirt is hideous. Covering such large area is probably costly too.

RE: House's backwall as retention wall

We don't know how much it would cost, especially in an area like that. Many of us would wonder why anybody would want to build a house there.

Your best source of cost might be the neighbor who has already done what you propose.

RE: House's backwall as retention wall

I'll look at the office tomorrow and see what I can find. The Texas department of transportation (TxDOT) publishes monthly what they pay for various types of retaining walls. It is called their low bid unit price report.

Their cost numbers are probably by cubic yard on something like that. It will not tell us how high the wall was though. I'll check at the office tomorrow and see if someone remembers what the cost was for the most recent large wall (cantilever and/or soil nail)

Here's a link to the TxDot website. Once you open the excel or text file, do a CTRL-F search for 'Retaining' to see all the wall types.

http://www.txdot.gov/business/letting-bids/average...

RE: House's backwall as retention wall

(OP)
Thanks!

What is the difference between Drilled/Grouted and Hollow Bar Soil Nailing vs Screw-in Soil Nailing?

Price seems to be so different between them

RE: House's backwall as retention wall

For Drilled/Grouted and Hollow Bar Soil Nailing, you drill a hole and then use cement grout to fix the nails into the ground.

For the Screw-in Soil Nailing, imaging a helical pile, no grouting. I think the name is self-explanatory.

RE: House's backwall as retention wall

(OP)
Interesting idea but I don't think that grass would do well in colder climate.

Sasa veitchii, Sasa bamboo, is probably better.

RE: House's backwall as retention wall

What did you decide to do? Looks like a retaining wall with a proper slope (similar to what your neighbor did) is the way to go. I would add some erosion protection for the slope (vegetation and/or geosynthetic mat).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources