short circuit current and soft loading - for equipment evaluation analysis.

short circuit current and soft loading - for equipment evaluation analysis.

(OP)
I am doing an arc-flash study. Here is the situation I am coming across and am trying to see how to go by it and understand it.
when analyzing the closed transition scenario (utility parallel to generators), few breakers are failing Equipment Evaluation. However, the client is saying there is soft-loading and the time is limited to 20sec, so not to include this closed transition scenario.

My understanding is that soft loading is for transfer of loads from one source to another. If for 20sec (during soft loading) the system will be in closed transition, I would think we would have to analyze this closed transition scenario for equipment evaluation when doing arc-flash study. Am I correct in saying soft loading will have nothing to do with the short circuit calculation in an event of a fault at 20second or less.
Any suggestions pls..............

RE: short circuit current and soft loading - for equipment evaluation analysis.

Any closed transition (milli-seccond or multi-second) should include both source contributions for short circuit calculations and arc flash if it creates worst case.

Generally worst case for arc flash will be one source (lowest fault current).

RE: short circuit current and soft loading - for equipment evaluation analysis.

(OP)
Thanks Ron. Yes that was my understanding for both source contribution for SCC calculation for closed transition.

RE: short circuit current and soft loading - for equipment evaluation analysis.

I believe that the initial transient fault current will be the same.
After the initial transient, the type of governor action and control may have an influence.
If the generator has field forcing to support short circuit currents, it will make a difference.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: short circuit current and soft loading - for equipment evaluation analysis.

For equipment evaluation (fault rating) purposes, you would have to consider the systems in parallel. For arc hazard, you could restrict any maintenance activity that could cause an arc flash during the closed transition.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close