Brownstone foundation wall
Hi All,
We are working on an existing brownstone and are adding some additional backfill to the exterior of the front foundation wall, in turn increasing the soil loads on the wall. In going through the calc I am finding the wall is not close to working, even for the existing condition.
Here is an example:
Say you have a 10ft tall foundation wall, 16" thick. This is a 3-story brownstone, so lets say the exterior wall above is 12" brick, and when accounting for windows has an average weight of 100psf. The floor framing typically runs parallel to the front and back walls, so no additional floor dead load. This gives a dead load of 30ftx100psf=3,000 plf.
Assuming a 16" thick foundation wall and that the dead load acts through the centroid of the wall, the overturning resistance is 3,000lbs x 16"/2=24,000 lb-in=2,000 lb-ft.
Just looking at the soil loading with an equivalent fluid pressure of 60pcf, we have a moment of Msoil=.128*(60pcf x 10ft x 10ft/2)*10 ft=3,840 lb-ft.
With out any factors of safety applied or including surcharge and seismic loading, we have a resisting moment of 2,000 lb-ft vs 3,840 lb-ft applied.
This would appear to be a very common wall in these parts, am I missing something here??
Thank you.
Here is an example:
Thank you.
RE: Brownstone foundation wall
The moment equation in my original post is the max moment for a pinned=pinned beam with a triangular loading.
Thanks.
Not a structural engineer; however.
f-d
ípapß gordo ainÆt no madre flaca!