Performance of heat exchanger
Hi All
I need to do an evaluation of a pilot plant heat exchanger that we have installed and see if it would be better suited than our current bigger installations. I was trying to calculate the effectiveness of the heat exchanger but I keep on getting 1 with the NTU method. Below is the information that I have so any suggestions on how to do this would be greatly appreciated. It is a counter flow plate heat exchanger.
Steam pressure in = 120 kPa
Steam Temperature in = 400 C
Other fluid temperature in = 110 C
Steam flow in = 0.278 kg/s
Other fluid flow in = 1.806 kg/s
Heat Transfer Coefficient = 2.5 [kw/(m^2 C)]
Contact Area = 40 m^2
Steam heat capacity = 2.07 kJ/kg K
Other fluid heat capacity = 3.91 kJ/kg K
I would appreciate your help.
RE: Performance of heat exchanger
Is the steam exiting as steam or water?
How did you get you heat transfer coef? Calculated?
Yes the steam is exiting as condensate water.
Yes the transfer coefficient was calculated when the trail was done.
I hope this helps.