DC Motor Performance

DC Motor Performance

DC Motor Performance

(OP)
I have a 2800 kW separately excited bidirectional DC motor which is drawing more armature current in one direction (when accelerating a given load) than in the other.  Field current limits are identical in both directions.  The armature converter is a series/parallel conencted device, which can source or sink current in one direction only (non-reversing armature circuit).

The load (required torque both directions) is identical.

The motor was recently replaced, which makes me wonder whether the brushgear has been set to the correct position with respect to the stator's neutral axis.  Any thoughts?

RE: DC Motor Performance

Hi, you don't say how much difference there is between the directions. generaly speaking torque is proportional to current, all other things being equal. Did you measure the torque in each direction or are you assuming that it's the same? If the brushgear is out of alignment you will see arcing.

RE: DC Motor Performance

(OP)
Hi, thanks for replying.

The armature current in each direction is approximatley 5900 and 6300 amps respectively.  This is with an equal current limit on the field converter in both directions.  The current limiting protection will trip the DC converter if the current exceeds 6200 A for more than about 5 seconds, so you can see our concern here.

The application is a mine winder, so direct measurement of torque is difficult, however, the payload in each skip is measured and is identical.  I have no reason to believe that one skip + its payload is any different to the other.  This was the case before the motor was changed out, and no current imbalance was apparent.

Yes, I agree we should see some sparking if the brushes are misaligned, but I am trying to find reasons why motoring in one direction should be different to the other.



RE: DC Motor Performance

Suggestion: The motor magnetic hysteresis curve (B-H) is supposed to be followed symmetrically in both directions to achieve the same motor output parameters in both directions.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources