Fire Tube Boiler Tube Plugging - Safe percentage of tubes plugged

Fire Tube Boiler Tube Plugging - Safe percentage of tubes plugged

(OP)
Fire tube Boiler

Total amount of tubes 257

57 Tubes Plugged = 20.8%

What is the ASME or industry standard with regards to the amount of tubes plugged before it becomes unsafe to operate.

Thanks

Steve M

RE: Fire Tube Boiler Tube Plugging - Safe percentage of tubes plugged

There is no guidance from the code of construction because this boils down to a performance issue, and each manufacturer would have their own performance/design criteria.

RE: Fire Tube Boiler Tube Plugging - Safe percentage of tubes plugged

Have you de-rated the unit?
If not then you likely are running too hot and at too high of a flow in the remaining tubes.
Accelerated wastage and the higher risk of tube failure are real issues.
In many systems 10% is not a problem, but above that things can get out of proportion, so many plants limit it to 15%.

= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, Plymouth Tube

RE: Fire Tube Boiler Tube Plugging - Safe percentage of tubes plugged

Suggest you contact the Jurisdictional Authority where the boiler will be installed to discuss. Get confirmation in writing and keep in file. If it were me I would also contact the Insurance company who will be insuring the boiler. Better safe than sorry.

RE: Fire Tube Boiler Tube Plugging - Safe percentage of tubes plugged

21% of the tubes plugged suggest boiler retubing as things can only get worse as indicated above remaining good tubes will get overheated and they will excessively expand in relation to the boiler shell and start leaking at the tube ends unless as suggested you reduce the firing rate.. I would like to know is there a pattern of the tube tubes leaking.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close