Serviceability vs. Minimum Wind Load

Serviceability vs. Minimum Wind Load

Serviceability vs. Minimum Wind Load

(OP)
I have a 20ft tall structure with walls on two sides which are all glass. As such, I was checking serviceability wind drift. I used the AISC 7 commentary with 10yr MRI which gives me a wind pressure qz of 10psf. According to AISC commentary, this pressure (Wa) is non-factored, so the full 10psf would be used.

However, AISC also has a requirement for a minimum wind load of 16psf. My guess is that this would not apply to serviceability, but the commentary doesn't address this.

RE: Serviceability vs. Minimum Wind Load

Quote (vmirat)

My guess is that this would not apply to serviceability, but the commentary doesn't address this.

I would be inclined to agree.

Quote (vmirat)

However, AISC also has a requirement for a minimum wind load of 16psf.

I'm not familiar with this. For my own edification, could you point me to the clause?

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Serviceability vs. Minimum Wind Load

Sounds like you're using the latest AISC (though I've never seen them mention a wind load) and an old ASCE 7. In ASCE 7-10 isn't the minimum wind load 16 psf?

RE: Serviceability vs. Minimum Wind Load

ASCE 7-05 (and older): Min 10 psf with Load Combination factor of 1.0 = 10 psf [net].
ASCE 7-10 (and newer): Min 16 psf with Load Combination factor of 0.6 = 9.6 psf [net].

In both cases, make sure you consider the 0.7 factor for components and cladding provided in the notes of deflection limits of the IBC. In the 2012 and newer versions of the IBC, it is a 0.42 factor on the nominal wind pressure, or another way of thinking is still using the 0.7 factor on the factored wind pressure: 0.7*(0.6*W) = 0.42W.

... Sorry if the above was not clear. You can take the 0.7 on the 10 [9.6] psf minimum net pressures when checking serviceability.

Juston Fluckey, SE, PE, AWS CWI
Engineering Consultant

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources