Earth current limiting Resistor

Earth current limiting Resistor

Earth current limiting Resistor

(OP)
I work at an old mining installation that uses reactors on the star point of all underground transformers to limit earth fault currents. Why use a reactor instead of resistors? I would have thought reactors would create problems with transients/harmonics during earth fault protection switching.

Any thoughts??

RE: Earth current limiting Resistor

Reactors actually work better at transients than resistors. The more rapid the change in current(di/dt, which in this case you can think of as a higher system frequency) the higher the impedance of a reactor.

RE: Earth current limiting Resistor

Reactors actually work better at transients than resistors. The more rapid the change in current(di/dt, which in this case you can think of as a higher system frequency) the higher the impedance of a reactor.

RE: Earth current limiting Resistor

Reactance grounding is not used much any longer.  The main drawback is the risk of transient overvoltages during faults.  To limit the overvoltage conditions, the fault current needs at least about 25% of the normal value.  This can still be a lot of current.  

Resistance-grounding can provide much greater reduction of fault current without overvoltage concerns, so it has basically replaced reactance-grounding, particularly for industrial facilities.

RE: Earth current limiting Resistor

DPC-

From my perspective, there still seems to be quite a bit of use for neutral grounding reactors. In fact, I dare say, it seems there has been an increase over the past few years, for reasons that I am not sure of. Clearly more folks use resistors than reactors, but there are certain applications where a reactor is clearly superior, particularly in EHV applications, where the inherent line capacitance is high.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources