HSS "ROUND" COLUMN
HSS "ROUND" COLUMN
I am interested in the capacity of HSS "round" columns, readily available to fabricaters in the Northeast USA. I was wondering:
1) the maximum wall thickness available with a 3" dia. column, 3 1/2" o.d. max?
2) the maximum allowable load, for the above column, tabulated by AISC given,
a) 10' unbraced in both axis
b) pin-pin connection
c) no eccentricity
Thanks so much
c) no eccentricity
Thanks so much
RE: HSS "ROUND" COLUMN
DaveAtkins
This may not be practical for longer pieces, but I have seen it done for larger sizes of pipe (e.g. 10"xxstrong) used in special applications.
The problem I ran into was that I specified the DBLX strong column and the steel manufacturer was suggesting the column was difficult to obtain and very expensive.
I usually spec. out pipe or square HSS tubing. I was not sure of round HSS or the allowable capacities. I found these capacities both for LRFD and ASD on the Steel Tube Institute web site. One interesting comparison between the round HSS column and the Extra Strong Pipe column is as follows:
3.5" OUT. ROUND CLMN (50 ksi) 3" EXTRA STRONG (36 ksi)
6' 63 KIPS 52 KIPS
7' 57 KIPS 48 KIPS
8' 51 KIPS 45 KIPS
9' 45 KIPS 41 KIPS
10' 38 KIPS 37 KIPS
11' 32 KIPS 33 KIPS
12' 26 KIPS 28 KIPS
13' 23 KIPS 24 KIPS
14' 19 KIPS 21 KIPS
The comparison between comparable thicknesses shows the HSS round a stronger column up until the 10'-11' length. At that point the Extra Strong Pipe is stronger.
Eventually I will do the calculation for my own comparison.
Anyway, FYI I called two Steel Manufacturers regarding the availability of a DBLX strong column. Both of them located the columns and gave me a tentative price within a day. The price was about .45 cents a lb, which to me seems reasonable.
Mark