Stupid question, but I have an application going into a 690v 3 phase system, so since the actual voltage to ground on any of the 3 legs is 690/sqrt3 = 398.4v using 600v rate wire is ok right?

RE: 690v 3 phase application lead wire rating

You have over 600 Volts phase to phase. Use 1000 volt rated wire.
My code requires wire to be rated for the highest voltage present, NOT the highest voltage to ground.
Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 690v 3 phase application lead wire rating

(OP)
TBE, in regard to the peak voltage versus RMS, wiring ratings are RMS values, so I don;t believe that is an issue.

Waross, if each individual wire is rate at 600v between the inner conductor and (in this case) the out SST armor (i.e. ground), then having 2 cables next to each other (i.e. the 690v) has 2 layers of said insulation. The problem comes in that this is specialty wire that is not available in 1kV rated. Is my thinking way off here?

RE: 690v 3 phase application lead wire rating

RMS values are used for cable voltage ratings.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 690v 3 phase application lead wire rating

BMG; I believe the concern is one cable insulation damaged or cable running across or touching a different phase lug would land you seriously underrated.

Keith Cress
kcress - http://www.flaminsystems.com

RE: 690v 3 phase application lead wire rating

Is this armored shipboard cable? MIL-C-24643 specs a 1kV rated single conductor armored wire. LSSSGA

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close