Need PF (power factor) meter for 11 KV
Can someone please recommend a PF meter that will work on 11 KV delta feeders (about 6400 v per phase)?
Some of our generators are reading a low power factor (80-85%). But because the generators are switched around to feed different feeders, it would make sense to correct our PF at the feeders. So my goal is to measure PF at the feeders, peak and off peak, and then I can size a capacitor bank that can be manually switched in and out by day-part. This is a small system 25 MW, about 25 Caterpillar 3500 series generators. Currently our feeders only have CTs to measure their current, but no PF measurement. Thanks for your advice :)
RE: Need PF (power factor) meter for 11 KV
But David's answer may be the more professional approach.
Bill
"Why not the best?"
Jimmy Carter
I would think you could get away with something like the Shark 200 meter. But if you want to get fancy you could go with the high end Nexus 1252.
https://electroind.com/product-info/shark-200-data...
https://electroind.com/product-info/nexus-1252-pow...