Simple Shear Connection w/ Axial Load W Beam to HSS Column
I have connection to be designed between W24X55 beam and HSS10X10X5/16 column. Vertical shear load is Vf=135kips and axial load is Pa=130kips. Double angle clip is not an option due to considerable axial load. Longitudinal through plate connection is not sufficient as hss wall plastification limit state is not satisfied. I`m considering a T-Stub with 1/2" thick longitudinal plate although it would need to be welded all round to avoid any torsion in vertical welds. Second option would be a single angle clip welded along heel with full return at top and bottom as shown in CISC Steel Construction Manual.It would be much appreciated if you could share any other ideas for this type of connection.
RE: Simple Shear Connection w/ Axial Load W Beam to HSS Column
It goes to another W24X55 beam with chevron bracing. See attached snapshot of partial roof plan at this location.
Through plate sounds like the way to go to me. Not sure what the plastification issues are as the tension should really pass through the joint without ever really touching the column.
Yes, the beam actually supposed to run over the top of column. This way there is no issue with transfering axial load at this location.
KootK
I was looking at the beam connecting to the external column which is part of the framing for precast wall system. There was no chevron bracing at that time so through plate connection at external column didn`t work because of wall plastification.
Thank you everyone for your comments.
Dik
Dave
Thaidavid
Weld as required to the column cap plate keep your unbraced length to a minimum (2" +/-) and continuous welds to the beam flange to get the loads in/out of the plate.
In this way, the axial force is transferred from beam to beam independently of the column walls or shear loads.