Restricted earth fault protection

Restricted earth fault protection

(OP)
Gents (and ladies),

What factors would you take into account when deciding to deploy REF protection to a transformer?

RE: Restricted earth fault protection

Assuming that you're already committed to using a relay rather than fuses, the only questions would be whether or not the transformer has a neutral (isn't a delta-delta transformer) and whether or not all of the necessary CTs exist. Beyond that deploying REF is simply turning it on and including it in the trip equation.

RE: Restricted earth fault protection

See section 16.7 of "Network Protection and Automation Guide" by Areva for an explanation on the uses of restricted earth fault protection. It depends on your system, grounding method, transformer size, how sensitive you want your differential elements, etc.

RE: Restricted earth fault protection

REF does provide more sensitive protection for some kinds of faults. However, there is a nominal cost of understanding how to properly set and test the REF element. Just because an element is available from the relay, it doesn't mean you have to use it.

RE: Restricted earth fault protection

(OP)
Hi,

I should have made myself clearer.

What factors would lead you to add or omit restricted earth fault protection in a particular situation ?

RE: Restricted earth fault protection

REF is more important with impedance grounded transformers because winding faults close to the neutral are harder to detect. The normal transformer differential protection will adequately protect solidly grounded transformers, but normally I would use REF if a neutral CT is available and the relay has the REF element built in.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close