Use of MVA (k>1) vs Current (K=1) interrupting rating breakers
With MVA rated (K>1) being a thing of the past more associated with older Switchgear and new current rated (K=1) being available for new Switchgear or breaker replacements why would anyone want to purchase/install MVA rated breakers for new Switchgear or breaker replacement in older Switchgear?
the reason I ask is that I notice that many of the major manufacturers still offer MVA rated breakers along with the newer K=1 rated breakers. Even when replacing breakers in existing switchgear I believe you can still replace the older breakers with newer K=1 rated breakers in the existing switchgear.
Are there any specific reasons or applications that would justify the use of an MVA rated breaker?
RE: Use of MVA (k>1) vs Current (K=1) interrupting rating breakers
After I posted this it just so happens that I was looking for a narrow frame MV vacuum breaker to replace and existing air break device and noticed that a particular manufacturer only offered this narrow frame breaker with an MVA (K>1) Total current rating.
Again this leaves me wondering why with the new vacuum technology would these MVA rated breakers still be offered as opposed to just the K=1 rated breakers. I thought the MVA rated breakers were a relic of air break devices that did not have the same interrupting capabilities that the vacuum breakers now have.
As long as the breaker has ratings that are suitable for your application, I would not be overly concerned about the test standard. Not sure why a "new" breaker would be rated on an MVA basis, but perhaps an offshoot of an older breaker that was originally tested under the older standard. Short circuit testing is expensive.