Coring holes in Double Tee top flange

Coring holes in Double Tee top flange

Coring holes in Double Tee top flange

(OP)
I've been looking for a guide on coring holes for mechanical ducts in precast double tee top flange, any recommendations on where to get that? I'm not finding anything on PCI website.

RE: Coring holes in Double Tee top flange

What size holes you thinking about?

RE: Coring holes in Double Tee top flange

(OP)
Up to 34". Center line distance btwn. flanges is 40". So pretty much takes the whole flange btwn. webs.

RE: Coring holes in Double Tee top flange

I would expect that to exceed any "guidelines" per se. I'd think that you'd have to check your flexure based on the reduced flange width available and do a little strut and tie to deal with reinforcing for the flow of forces around the opening. Whether or not it's a big deal surely depends where on the span you land.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Coring holes in Double Tee top flange

Likely too big... can you contact the precast supplier? Almost no flange left between the stems...

Dik

RE: Coring holes in Double Tee top flange

If it is toward the ends of the member, the moment and the corresponding flange stress due to flexure will be smaller and thus the flanges may not be as critical.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: Coring holes in Double Tee top flange

So the sheetmetal (HVAC ducts) is going to destroy the stressed load-bearing concrete flanges holding up the entire building? You're solving the wrong problem!

Yes, it will require the sheetmetal (actually, the flow calc's for the sheetmetal) to be analyzed instead of just picking out tubes from the book, but allow a row of 12" x 24" rectangular holes to be notched in the concrete at the joints between two adjacent flanged pre-cast members - 6 inch U-shaped notches in each of two paired beams. The sheetmetal - and, yes, I am insulting the sheetmetal ducts - is rebuilt to accommodate the plenum, plenum-to-rect, rectangular sections, and then the receiving plenums to allow the ducts to continue below the floor.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources