Transformer Copper Losses pu calcs

Transformer Copper Losses pu calcs

(OP)
I have a delta/wye transformer. I want to get transformer pu copper losses.

The transformer is 60MVA, 25/13.8 y/d, Z% = 10%, X/R = 23.5

Zb = V2/S = 13.8*13.8/S = 13.8*13.8/60 = 3.174 ohms
Xactual = Zb*Zpu = 0.3174 ohms
R = X / (X/R) = 0.013506383 ohms
I = V/Z = 13.8/SQRT(3)/SQRT(0.013506383* 0.013506383 + 0.3174 * 0.3174) = 25.07948924 kA
Ploss = 3*I2*R = 25.48576593
Ploss pu = 25.48576593/60 = 0.42476 pu??

or
Zb = V2/S = 13.8*13.8/S = 13.8*13.8/60 = 3.174 ohms
Xactual = Zb*Zpu = 0.3174 ohms
R = X / (X/R) = 0.013506383 ohms
P = V2/R = 13.8*13.8/0.013506383 = 13 MW??
Ploss = 14/60 = 24%

This does not make any sense. Can you please advise?

RE: Transformer Copper Losses pu calcs

The per unit copper loss will be based on the per unit current. It looks like you used a short circuit current instead of the base operating current.
60 MVA @ 13.8kV = 2510 amps = 1.0 per unit.

If your resistance calculations are correct P = I x I X R = 2,510A x 2,510A x 0.01350 ohms =85,089 Watts = 85kW
Per Unit = 85.089 kW / 60,000 kVA = 0.001418 per unit per phase. This would be for one winding, x 3 = 0.00425 per unit copper loss.

We get about the same answer using the 25 kV equivalent resistance and current.

While that number may be in the ball park, there are some inaccuracies due to: resistance changes with temperature, allocation of the resistance between the 25 kV "Y" winding and the 13.8kV delta winding and other effects. If you need to get accurate data, look at the factory test report that should show the measured load losses adjusted for operating temperature.

Or you could just use per unit. Zpu= 0.1 = sqrt(R^2 + X^2), and X/R = 23.5. X=23.5R.
Substituting for X: 0.1^2 = R^2 + (23.5 R)^2 = R^2 (23.5^2 + 1). Solving for R = sqrt (0.1^2 / (23.5^2 +1) = .00425.

I*I*R = 1.0 x 1.0 x .00425 = 0.00425 per unit copper loss.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close