Single Family Roof Deck
I have a couple of town houses and duplexes that because of their size fall under IBC. They have roof decks/terraces and I would like to design these for a Live Load of 40psf. I am going to hang my hat on the on IBC Table 1607.1, Residential, One and Two Family Dwellings, All other areas = 40psf. Recognizing that the same table lists roof loads used for assembly purposes = 100psf.
Chapter 16 does not appear to define what "assembly purposes" means. Assembly is defined in Use/Occupancy and limits are established, less than 50 people being one exception. However, in that exception, they list the occupancy to be Group B which does not apply.
Is there a clear defensible position to use 40psf for roof decks in a single family home?
RE: Single Family Roof Deck
However, at least in California, you are required to use 1.5 x occupancy served now due to an emergency regulation put into effect. This regulation was a reaction to the Berkeley Balcony collapse.
https://www.documents.dgs.ca.gov/bsc/Info-Bulletin...
Aside from the long term weathering of the supports, the loading is often not uniform. People congregate at the perimeter of the deck (or rooftop).
I would go with 60-75psi and sleep easy at night.
I think that it can be inferred that the AWC position is that ASCE7 requires 100psf.
Our office designs large public decks for 100psf.
We design all other decks for 65-75psf.
He designed them at 75 PSF, if the client complained he would suggest designing one that only projected 30".
He was also a stickler for building attachment details.
Joel, reality is even worse, it is everyone running to outside edge of the deck to see what is happening.....
Dik
My condition is not hanging off the side of the building, it's on the roof in a single family home. I should be no more worried with the design live load if the party is on the roof deck or in the living room.