Arch Flash Hazard Analysis
Arch Flash Hazard Analysis
(OP)
Hi there,
For those that are familiar with the arch flash hazard analysis using SKM, Easypower, etc,
Is it possible to perform the analysis on section of the one-line without the full one line modeled?
I would imagine you would need the equivalent impedance? Comments?
For those that are familiar with the arch flash hazard analysis using SKM, Easypower, etc,
Is it possible to perform the analysis on section of the one-line without the full one line modeled?
I would imagine you would need the equivalent impedance? Comments?






RE: Arch Flash Hazard Analysis
Also be aware that any motor or generator contribution would need to be considered in that equivalent impedance, and you'd need to take care that the protective device you model would actually clear the generator/motor fault contribution in reality.