Rigid Roof Insulation Weight
ASCE states that rigid roof insulation weighs 1.5 psf per inch of thickness, whereas, polyiso insulation, like Thermax, is < 0.25psf per inch.
Is there a reason why ASCE might be so much heavier? Is it assuming some sort of saturation?
RE: Rigid Roof Insulation Weight
ASCE tabulated weight values are known to be conservative, if you can justify a lesser weight with documentation and you need that extra weight savings then feel free to do so
or just a catch all for any rigid roof insulation.
Dik
Maybe once the membrane is shot, they assume it absorbs water :>
I'm looking into this at the moment and stumbled across this thread.
I have no problem using the catch-all value for normal gravity design, my issue is with the wind uplift, you would want to use a more accurate value.
The ASCE number is way off compared to what is typically used for rigid insulation. Use a value based on whatever product they're specifying.
The 1.5 psf/in is consistent with lightweight insulating concrete. Rigid board insulation is much lighter.