I am designing the sprinkler system for a building with escalators that traverse multiple floors. As much as I would like to eliminate sprinklers from below the escalators, I don't think I can since they are greater than 4' wide. I attached a picture of a similar layout for the escalators to clarify. The floor opening around the escalators is much smaller in my case so I do have the vertical opening protection.
Am I missing anything here?
Am I missing anything here?





RE: Sprinklers below escalators
Where do you think the sprinklers should be?
RE: Sprinklers below escalators
RE: Sprinklers below escalators
What is the size of the opening
RE: Sprinklers below escalators
What the heck, how many more heads can it be?
RE: Sprinklers below escalators
RE: Sprinklers below escalators
NFPA 13 states sprinklers are required under stairways as well [8.15.3] but also refers to escalators as 'moving stairways' so I would install sprinklers beneath them.