Sprinklers below escalators

Sprinklers below escalators

(OP)
I am designing the sprinkler system for a building with escalators that traverse multiple floors. As much as I would like to eliminate sprinklers from below the escalators, I don't think I can since they are greater than 4' wide. I attached a picture of a similar layout for the escalators to clarify. The floor opening around the escalators is much smaller in my case so I do have the vertical opening protection.

Am I missing anything here?

RE: Sprinklers below escalators

How many floors will you have.

Where do you think the sprinklers should be?

RE: Sprinklers below escalators

(OP)
Four floors. I am thinking sprinklers would be required below the lowest level of escalatirs at a minimum, but again, I'm not 100 percent certain that they aren't required below additional levels.

RE: Sprinklers below escalators

Without scaled drawings I would say your answer is correct

What is the size of the opening

RE: Sprinklers below escalators

I think you should provide the sprinklers. I had this same issue at an airport. The Airport Code officials required it.
What the heck, how many more heads can it be?

RE: Sprinklers below escalators

Check with your fire marshal or fire department and the answer will be yes.

RE: Sprinklers below escalators

Definitely a fixed obstruction so sprinklers are required.

NFPA 13 states sprinklers are required under stairways as well [8.15.3] but also refers to escalators as 'moving stairways' so I would install sprinklers beneath them.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close