Obstruction in front of louvers

Obstruction in front of louvers

(OP)
For a project I'm working on, there is a 8.75' x 6.5' acoustic intake louver that might have a 3' tall planter located 10" from the louver. The airflow is 13,000 cfm and the face velocity is 508 fpm. Is there enough room between the planter and the louver? Is there a minimum distance that objects need to be separated from a louver?

There is also have a 8.75' x 6.5' acoustic exhaust louver that might have a sign covering the whole louver and be 2' in front of the louver for aesthetic purposes. The air flow is 13,000 cfm and the face velocity is 508 fpm. Is this enough distance from the louver to get the proper airflow? And again, is there a minimum distance for objects in front of a louver?

RE: Obstruction in front of louvers

Tell the architect that you need to increase the louvre area by 50% or move the planter by 3 ft!

RE: Obstruction in front of louvers

(OP)
Is that because of the pressure loss by the planters would be excessive or is there another reason? How much pressure loss would the planters cause?

How about the sign in the second example? Would the sign cause a problem?

RE: Obstruction in front of louvers

There are a number of possible issues, for which you need to consult someone familiar with HVAC:

> 13000 cfm / (8.75' * 6.5') = 228.6 fpm, the lower flow is good, less of an issue with noise and leaves getting sucked into the louvers
> noise
> hypothetically, you need something like 1 object diameter's separation for the flow to return to normal: https://github.com/timhutton/latticegas. Otherwise, you will likely get a noisier system

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm

RE: Obstruction in front of louvers

It's 229 fpm as per IR.

The questions:

Yes.
No.
Yes.
No.

RE: Obstruction in front of louvers

Stop looking here for free Engineering and hire an Engineer who does this.

RE: Obstruction in front of louvers

(OP)
What is meant by "1 object diameter's separation"? What is the definition for "object". I am am a pump and piping engineer so I understand such things as 10 pipe diameters needed in front of a flow meter is required to straighten out the flow. Is this basically the same thing? I tried to estimate the pressure loss for the sign scenario by assuming that the flow around the sign would be equivalent to a 90 degree bend though a 50" diameter pipe flowing at the same velocity as around the sign. I got less than 0.1 wc. Is this a valid method?

RE: Obstruction in front of louvers

(OP)
It is also helpful to know that this is ventilation for a emergency generator in a building. It would not be a constant ventilation but would happen approximately for a half hour every two weeks for testing. And during emergency conditions.

RE: Obstruction in front of louvers

Quote (Ron757)

I am am a pump and piping engineer... Is this basically the same thing?

Yes, but since air is compressible and liquids are not, the problem is complicated, not basic. The fan type and operating characteristics are more important than louver dimensions. Is there one fan, or two (one intake, one exhaust). The technical information from the fan manufacturer needs to be evaluated to see how sensitive fan operation is to airflow disruption.

IMHO, the planter in front of the intake is a small problem. The sign just outside the exhaust is a big problem.

www.SlideRuleEra.net idea
www.VacuumTubeEra.net r2d2

RE: Obstruction in front of louvers

(OP)
Thanks SlideRulerEra for the information. Yes, I realize the some differences between liquids and air. I used a chart that takes into account pressure, temp and flow in determining the pressure loss. But not familiar with effect on fans, etc. I am from the slide ruler era too. I am helping someone else on this so I will have to find out the location of the fans. I think this problem is interesting.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close