Transformer Connection 3PH Open Delta 480V w, 2-Bushing Xfmrs
Transformer Connection 3PH Open Delta 480V w, 2-Bushing Xfmrs
(OP)
We have some 2-bushing 277/480V overhead transformers in stock and would like to use them to install a 480V open delta bank (versus using 3-bushing transformers that have a center tap, which we don't have in stock). I'm not a transformer connection expert, but I'm thinking I can delta-connect two 2-busing 277/480V transformers and run the 3 legs for a 3-wire 480V service. I took a stab at the attached electrical diagram, but I'm wondering if the winding polarity will give me the correct voltage.






RE: Transformer Connection 3PH Open Delta 480V w, 2-Bushing Xfmrs
RE: Transformer Connection 3PH Open Delta 480V w, 2-Bushing Xfmrs
RE: Transformer Connection 3PH Open Delta 480V w, 2-Bushing Xfmrs
But if ANYTHING in their facility is using 480V 3 phase input to a power conversion device, such as a VFD, servo, UPS, large 3 phase power supply etc., then open delta is a disaster waiting to happen, and the preventative medicine for that is to create a solidly grounded wye system, even if you never use a Line to Neutral connection on it.
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
RE: Transformer Connection 3PH Open Delta 480V w, 2-Bushing Xfmrs
RE: Transformer Connection 3PH Open Delta 480V w, 2-Bushing Xfmrs
Jeff, I understand that he is going from delta to wye. From that perspective, your answer will be correct in that safety issues will be with the existing delta system, not the proposed wye system.
The safety issue may be if a customer has a ground fault on an ungrounded delta system that he has neglected to repair.
The first warning of the failure will be the ground detector system.
If the customer chooses to ignore that indication of a failure, the second indication of failure will be more dramatic when the grounded wye system is connected.
You may want to have the customer sign a disclaimer before energizing the new transformer bank.
Sign now and the power will be on in a few minutes.
Decline to sign and the proper transformers are on back order and the power will be on in about 6 weeks when the new transformers arrive.
Bill
--------------------
"Why not the best?"
Jimmy Carter