Add fans to transformer

Add fans to transformer

(OP)
We have a 480-208/120v,
 
1000/1333 KVA transformer with load running close to its OA rating. We decided to install custom made fans, such that air is forced to go through windings. I know this might not equal it's FA rating, but how can we calculate new rating? we can measure all peremeters including KVA, current, temperature...etc.

RE: Add fans to transformer

I am surprised that the forced-air ratings are not provided on the NP. I would suggest that you ask the OEM for the ratings. Don't forget that these ratings are also affected by the ambient temperature, insulation class and temperature rise.

"I have not failed. I've just found 10,000 ways that won't work." Thomas Alva Edison (1847-1931)

RE: Add fans to transformer

FA ratings only exist when the transformer manufacturer designs the FA system.

RE: Add fans to transformer

(OP)
Thanks guys. The FA rating is 1333 KVA, but as David beach said, this only true when we use vendor provided fans. My question is, if we know know the difference in temperature those fans provided, can we calculate the new rating? For example, if we able to lower the temp by 20 degree C, how much KVAs did we gain? I guess I can look at KVA Vs Temp graph, and figured out a correlation that way...any thoughts?

RE: Add fans to transformer

I think you are considering dry type transformers. Here normally they use special fans and blow air upwards through the gap between HV and LV windings. You must get guidance from the OEM. As regards loading margin for lower temperature rises etc, please refer loading guides for dry type Transformers. Refer to IEC 60076-12(2008) or C57.96-2013

RE: Add fans to transformer

Perhaps I'm missing something here, but you cannot force air through the windings of an oil filled (OA/FA rated)transformer. Air doesn't have sufficient dielectric strength.

RE: Add fans to transformer

Howdy Steve,
I understand that the transformer in question is a dry-type, and not oil-filled.
GG

"I have not failed. I've just found 10,000 ways that won't work." Thomas Alva Edison (1847-1931)

RE: Add fans to transformer

OA stands for Oil-Air, both unforced without the F. A dry type would have AA/FA ratings with the AA meaning ambient-air.

RE: Add fans to transformer

Select a max temp, say 150C. Don't go over the max temp on the nameplate.
Add load until you reach that temp, with fans running.

To be on the safe side, put 4 fans per winding, 2 on the front, 2 on the back, for a total of 12.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close