combustible space sprinkler req.
It is a building with roof trusses and drop ceiling. 5/8" drywall attached to bottom of trusses.
Do we need protection above ceiling?
I attached pdf from arch. drawings.
RE: combustible space sprinkler req.
If so yes sprinkler protection is required.
Unless you fill the Entire space with non combustible insulation.
In the picture you provided, you are going to require SPECIALLY LISTED concealed space sprinklers. These come with their own requirements in the sprinkler data sheet.
You will possibly need draft curtains (not draft stops) depending on full height walls and such.
Review the criteria carefully on those sprinklers.
Travis Mack
MFP Design, LLC
www.mfpdesign.com
"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/9221...
Does not matter, but what is the use of the building??