Transformer Nameplate

RE: Transformer Nameplate

It is a multi LV Transformer 66/34.5-12.47 kV and impedance will change at different voltage ratios. In the impedance table the voltage ratios and MVA shall be shown. In this case it is difficult to guess.

RE: Transformer Nameplate

The four impedances look to be:
10 MVA / 69 kV-34.5 kV: pos = 5.04%, zero = 5.04%
12.5 MVA / 69 kV-34.5 kV: pos = 6.31%, zero = 6.30%
20 MVA / 69 kV-12.47 kV: pos = 9.71%, zero = 9.86%
25 MVA / 69 kV-12.47 kV: pos = 12.28%, zero = 12.32%

The 34.5 kV impedance is almost half that of the 12.47 kV impedance because of the change in base.

The 12.47 kV winding is made up of three equal winding sections that are connected in parallel. These same winding sections are connected in series to give 37.41 kV. A small section of one of the winding sections is left out of the circuit so that you get 34.5 kV rather than 37.41 kV as the nominal voltage. This small missing section is why the 34.5 kV impedance is not quite half of the 12.47 kV impedance.

RE: Transformer Nameplate

I don't think the short-circuit impedance is connected to secondary voltage but only with the rated power. If you'll take a look in IEC 60076-5 Power transformers –Part 5: Ability to withstand short circuit you'll see in Table 1 Recognized minimum values of short-circuit impedance for transformers with two separate windings the only parameter required it is the rated power kVA. So for 20-25 MVA minimum 8-10% is recommended. For 10-12.5 MVA -since these are the same windings connected parallel-and only two windings when for 20-25 MVA 3 series windings are used- it will be one half about, indeed.

RE: Transformer Nameplate

7anonter4,Generally your view is correct. But here, certain sections are kept floating during 12.47 KV connections ie there is no current flow in those sections. This changes the spatial ampere turn distribution and flux fringes out at those gaps, increasing the impedance.

RE: Transformer Nameplate

Thank you, prc.I agree.

RE: Transformer Nameplate

The IEC usually uses the highest values rather then the base.

RE: Transformer Nameplate

What is the difference between the 10 and the 12.5 rating? In the connections table, they are both listed as OA 55 degrees C rise. However, near the top of the nameplate the TYPE is listed as OA/FA.

RE: Transformer Nameplate

Generally in IEC world, percentage impedance is always mentioned on FA rating while in US it is based on OA rating. In this case NP shows impedances both at OA &FA ratings,but with out clearly indicating the base MVA or voltage rating. Indications given by mgtrp seems correct.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close