PowerWorld Doubt

PowerWorld Doubt

(OP)
Hi,

I am Maria. I am working in a project with PowerWorld and I am not able to get transient stability results.

I use a simple system, whose raw file is:
0, 100.00 / PSS/E-33.2 SUN, MAR 10 2013 17:41


1,'BUS1 ', 345.0000,3, 1, 1, 1,1.04000, -0.0000,1.10000,0.90000,1.10000,0.90000
2,'BUS2 ', 345.0000,1, 1, 1, 1,1.01613, -3.3252,1.10000,0.90000,1.10000,0.90000
0 / END OF BUS DATA, BEGIN LOAD DATA
2,'11',1, 1, 1, 0.000, 0.000, 0.000, 0.000, 103.130, -37.617, 1,1,0
0 / END OF LOAD DATA, BEGIN FIXED SHUNT DATA
0 / END OF FIXED SHUNT DATA, BEGIN GENERATOR DATA
1,'1 ', 106.496, 45.996, 300.000, -300.000,1.04000, 0, 100.000, 0.00000E+0, 1.73300E-1, 0.00000E+0, 0.00000E+0,1.00000,1, 100.0, 999.000, 10.000, 1,1.0000
0 / END OF GENERATOR DATA, BEGIN BRANCH DATA
1, 2,'1 ', 1.00000E-4, 5.76000E-2, 0.00010, 250.00, 250.00, 250.00, 0.00000, 0.00000, 0.00000, 0.00000,1,1, 0.00, 1,1.0000
0 / END OF BRANCH DATA, BEGIN TRANSFORMER DATA
0 / END OF TRANSFORMER DATA, BEGIN AREA DATA
1, 1, 0.000, 10.000,' '
0 / END OF AREA DATA, BEGIN TWO-TERMINAL DC DATA
0 / END OF TWO-TERMINAL DC DATA, BEGIN VSC DC LINE DATA
0 / END OF VSC DC LINE DATA, BEGIN IMPEDANCE CORRECTION DATA
0 / END OF IMPEDANCE CORRECTION DATA, BEGIN MULTI-TERMINAL DC DATA
0 / END OF MULTI-TERMINAL DC DATA, BEGIN MULTI-SECTION LINE DATA
0 / END OF MULTI-SECTION LINE DATA, BEGIN ZONE DATA
0 / END OF ZONE DATA, BEGIN INTER-AREA TRANSFER DATA
0 / END OF INTER-AREA TRANSFER DATA, BEGIN OWNER DATA
0 / END OF OWNER DATA, BEGIN FACTS DEVICE DATA
0 / END OF FACTS DEVICE DATA, BEGIN SWITCHED SHUNT DATA
0 / END OF SWITCHED SHUNT DATA, BEGIN GNE DATA
0 / END OF GNE DATA, BEGIN INDUCTION MACHINE DATA
0 / END OF INDUCTION MACHINE DATA


And I attach de dynamic PVD1 model (a distributed PV system model) to the generator in bus 1, using the default parameters. However, when trying to run de transient stability, an error appear in the second 0 saying:

Number of Viable Islands Changed from 1 to 0
No Viable Islands -- Solution Aborted

The island is:
Slack Bus Number Slack Bus Name Total Buses Energized Gen MW Gen Mvar Load MW Load Mvar Scheduled Exports DC MW Exports
1 BUS1 2 YES 106,5 46,0 106,5 38,8 0,0 0,0

I don't get why the island is not viable. I don't know why it doesn't meet the criteria or what is happening...I have found the criteria are:
1. At least one island bus has some on-line generation with a positive Maximum MW Limit and is NOT set to regulate the voltage at a bus in another island.
2. At least one island bus has a closed load (Note: It could still be a 0.0 MW load) OR the island is connected to another island by a DC transmission line.

If anyone could help me I would be so grateful. I am completely stuck.

Thanks,

Maria

RE: PowerWorld Doubt

You might be way beyond this but I followed Overbye's transient power presentation to carry out transient analysis in Powerworld. The powerpoint presentation literally baby steps you through the whole thing. I don't know if this solves your problem or answers your question, though.

https://www.slideshare.net/JoeloRoss/powerworld-15...

RE: PowerWorld Doubt

(OP)
Thanks for answering. I have already looked that presentation, and I know the procedure to run a transient analysis, but I still cannot solve my problem. Thanks anyway!

RE: PowerWorld Doubt

@HamburgurgerHelper: Can you download and attach this file so it can be downloaded by others on this site if possible? I'd like this for future reference and I don't want to make an account which will spam my Email. That is of course assuming you already have. Or know a way without spam.

RE: PowerWorld Doubt

Mbrooke,

You should start using anonymous proxy email servers for one off stuff that you don't want any spam from. Just pick an email address name, sign up for whatever site, and click on the email address confirmation email. If you need to reset your password or whatever, just keep note of the name of your dummy email account.

http://www.quertime.com/article/16-online-services...

Here is an link to the powerpoint file.

http://powerprotection.wikia.com/wiki/Transient_An...

RE: PowerWorld Doubt

Good advice- I will use this in the future. Maybe its my end, but I can't seem to access the file on wikia?

RE: PowerWorld Doubt

Question- the downloaded file is supposed to open with Powerpoint, correct?

RE: PowerWorld Doubt

It works now! And thank you for putting up with me making this more difficult then it really was lol- I owe an apology in regards to that. And I owe you several favors now :)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close