Underhung 220 kV surge arrestors

Underhung 220 kV surge arrestors

(OP)
Rarely to see, but it seems necessary in a tight substation to install surge arestors under gantry beam, is there any special requirements for that?

Does it need any special manufacturing or just to be mounted in inverted vertical position?

The center phase may have a longer grounding wire with one 90 degree bend.

RE: Underhung 220 kV surge arrestors

We had an under hung 115 kV arrestor fail several years ago. At the time, there was vigorous debate as to whether the mounting allowed water to penetrate the joint between the sheds and the base. Unfortunately I don't remember if there were definitive conclusions.

RE: Underhung 220 kV surge arrestors

(OP)
Good point.

These SAs were porcelain or silicone polymer housed?

RE: Underhung 220 kV surge arrestors

The insulator shed design will likely be different for under-hung. Consult the manufacturers manual for details of permissible mounting angles. Avoid using the arrester as a jumper or dropper support so that it can be disconnected easily if it fails, and the main power circuit can quickly be restored to service.
Regards
Marmite

RE: Underhung 220 kV surge arrestors

Agreed with the above in terms of the possibilities of failure and the ease of replacement. We recently installed underhung arresters due to a limitation of space. The preference is to go with composite housings, but some utilities do not accept these. The risk of catastrophic failure is higher with porcelain housings over composite housings. The shed profile will be different,as explained above, with the shed angled towards ground in its inverted position. The arrester grounding lead will be physically (unless it's insulated?) connected to the frame of the gantry, and if I'm not mistaken, this will lower your inductance and lower your resistance compared to an insulated ground wire.

RE: Underhung 220 kV surge arrestors

(OP)
Good point qman5

I think the utility will require an insulated conductor down to ground grid but what if the gantry frame is used as a down conductor? I doubt the inductance and reistance won't be predictable compared with a physical lead.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close