Gas Pipe Sizing
Gas Pipe Sizing
Gas Pipe Sizing
Good Morning,
Could anyone help me to find the formula to design the pipe diameter and thickness if I know the pressure, temperature, CFM, type of gas and length of pipe?
RE: Gas Pipe Sizing
What do you require for fluid velocity? Once you determine that, use volumetric flow rate and velocity to get required cross sectional area (which will give diameter).
Are you moving the fluid a long distance (and worried about pressure drop)? Otherwise velocity and CFM will drive line size.
RE: Gas Pipe Sizing
Start with this lot - http://www.engineeringtoolbox.com/natural-gas-pipe...
Note that many online calculators etc are only valid for low pressure systems where Pin and P out only change by 10% or less
Thickness is from the relevant design code or material spec.
High pressure, long pipelines, large differences in Pin to P out are more complex, but often a rough approximation can be made or you divide your pipe into segments and iterate between them.
see https://www.lmnoeng.com/Flow/weymouth.php for a bit of an explanation
Did you do any research into this?
RE: Gas Pipe Sizing
Generally, the local AHJ has a code requirement, whether IFGC or the NFGC for sizing natural gas piping within a building.
Start there.
RE: Gas Pipe Sizing
Thank you.
I don't have the velocity. Following are rest of my parameters:
Pressure = 450 PSI
Pipe Capacity = 100 CFM
Pipe Length = 300 ft
Gas = Nitrogen
Yes, I did some research, but couldn't find out an appropriate answer.
RE: Gas Pipe Sizing
Look at the Darcy equation for compressible flow.
That is the best bet.
RE: Gas Pipe Sizing
To the pipe sizing, you still need either the desired gas velocity or pressure drop allowed for the 300ft pipe.
RE: Gas Pipe Sizing
If I have the velocity what equation I can use?
RE: Gas Pipe Sizing
The Crane tech paper #410 "Flow of Fluids" is good to have for the engineering reference.
RE: Gas Pipe Sizing
At that pressure your 100 cfm is about 3 cfm in the pipe. That's about 7.5 cu inches per second. So work out internal area of your pipe sizes and then velocity to see which pipe size works.