e7014 electrode used instead of specified e7018

e7014 electrode used instead of specified e7018

(OP)
A welder has substituted an e7014 electrode for the specified e7018 (low hydrogen) electrode for welding new A36 steel to existing gr 30 (older) steel. AWS A5.1 shows that the E7014 and E7018 have similar strength properties but the E7014 has no charpy v notch limits, unlike the E7018. Also E7014 can be susceptible to hydrogen embrittlement of the welds. The welds are fillets joining pieces less than 3/4" thick. The welds are fillets, 3/8" max to 5/16" min. The loads are static. The welds have been visually inspected and look ok, no cracks visible. Has anyone any experience about using E7014 in structural applications? All comments appreciated.

RE: e7014 electrode used instead of specified e7018

As long as impact requirements are not needed by design AND you perform a surface NDT (wet fluorescent MT) or Liquid Penetrant) of the E7014 welds to check for delayed or cold cracking you should be ok.

RE: e7014 electrode used instead of specified e7018

They both work well and I've seen both used effectively. The only difference I know of is that E7018's are low hydrogen, and, use a higher current and have a slightly higher deposition rate. Maybe someone else can add/correct.

Dik

RE: e7014 electrode used instead of specified e7018

Thanks metengr... didn't know that E7014's were susceptible to cold cracking...

Dik

RE: e7014 electrode used instead of specified e7018

You may need to qualify the procedure using the E7014 (change of F-No.) if you are not using a "prequalified" WPS. If you are using a "prequalified WPS, you will need to revise it to indicate the use of E7014 instead of E7018.

RE: e7014 electrode used instead of specified e7018

This appears to be an issue with proper training and a failure in supervision.

The welder should understand the differences between E7014 and E7018. That is a training issue.

The issue with supervision is another issue. We don't know all the details that would point the finger to someone that didn't do their job.

Was the welder a contractor working on a job site? If he was, did he have his own or was he provided with a WPS that provided the needed information? Was this job governed by a code such as an AWS structural welding code or ASME construction code? If the project was required to meet a code, who was responsible to review the WPS the welder used (or didn't use). Was the welder an employee? If the welder was an employee, who was the immediate supervisor?

The issue I'm attempted to circle around to is what is going to be done to ensure the same problem doesn't happen in the future. Additionally, what is going to happen to rectify the mistake that did occur. If the project is required to comply with a code, there may be ramifications other than whether the electrodes are equivalent. The simple answer is they are not equivalent in all respects. Many of the differences have been noted, but one has not been addressed. That difference is the F numbers assigned by either AWS or ASME. The two electrodes have different F numbers. The F number is an essential variable. Ouch! Again, if the project is required to comply with a code, there are code issues that have to be rectified.

It would be nice to know the whole story rather than interesting tidbits.

Best regards - Al

RE: e7014 electrode used instead of specified e7018

In addition to Al's comments, E7014 has different penetration characteristics. While the surface may appear sound, did full penetration occur? Are there bridged roots and lack of fusion unseen? The use of the wrong electrode is a nonconformance and should be fully evaluated.

RE: e7014 electrode used instead of specified e7018

Hi Samdamon,

The whole issue is a failure of Q.A system. No welder should indiscriminately change welding electrodes , without consultation with the welding or Q.A personnel. Small extract on E-7014 electrodes from Sec-II, Pt-C SFA 5.1 is as follows. The rest you may find in SFA 5.1 in the following clause.

A7.5 E7014 [E4914] Classification

A7.5.1 E7014 [E4914] electrode coverings are similar to those of E6012 [E4312] and E6013 [E4313] electrodes, but with the addition of iron powder for obtaining higher deposition efficiency. The covering thickness and the amount of iron powder in E7014 [E4914] are less
than in E7024 [E4924] electrodes (see A7.10).

In a nutshell these electrodes are Non-Low Hydrogen type electrodes. If the specification calls for "Low Hydrogen Electrodes" irrespective of the steels used then welds with these electrodes may be unacceptable,subject to the discretion of the client.

Thanks.

Pradip Goswami,P.Eng.IWE
Welding & Metallurgical Specialist
Ontario,Canada.
ca.linkedin.com/pub/pradip-goswami/5/985/299

RE: e7014 electrode used instead of specified e7018

You've got two separate problems here.
(1) a non-conformity with the specs
(2) a practical problem: the consequences of using a lower quality consumable than specified.

For (1), you need all documentation to see what exactly was asked. We can only give suggestions on what is commonly applicable, but the only way to know for sure is with all documentation on the table.

For (2), you can assess if what is actually performed, can be accepted or not. Depending on the circumstances, the weld may perfectly be accepted, even though 7014 was used.

We don't have enough information to assess either problem.

http://www.fusionpoint.be
http://be.linkedin.com/in/fusionpoint

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close